QUOTE(ckl1998 @ Dec 1 2021, 08:12 PM)
I see, the socket and the plug has to be the same amp. Based on my understanding on the page you shared and also in the context of Malaysia, if single phase, then blue plug and blue socket which is 3 pin, if it is 3 phase, then red plug and red socket which could be 4 or 5 pin. In my case, 3 phase, residential, how many pin should I go, 4 or 5?
Ultimately the determination will be based on the device (hob) input need
230V single phase or 415V 3 phase. This you need to check the hob sticker.If hob is
230V single phase and provide standard 3 wire LNE, then you need:
1. a blue plug, 3 pins, 32A socket+32A plug, choose IP44 or IP67 rating depends on how heavy duty w.r.t. oil n water splash consideration.
2. LNE Cables from DB to connection unit sizing for 25A hob min. 4mm² (support up to 32A limit). Budget ada, can use 6mm² (marginally more expensive but runs cooler when loaded). Mega Kabel recommended. 4mm² x 3 roll 100m should be around 580-600 bucks already. But as you're installing a few high power device then it make more sense for full roll. Loose cut can get expensive.
3. PVC box or metal box big enough to install the CEE socket and isolator switch. Keep CEE socket out of easy reach of kids as the CEE socket is an industrial tool, not a residential socket, as its holes are big enough to poke finger into. ⚠️
4. Salzer on off switch with correct nominal load rating (32A or bigger) eg
https://shopee.com.my/product/79031048/3576345371 in 32A, 2 pole version (cuts both L and N). E is wired direct from DB to socket.
5. MCB sizing to follow cable safe limit 32A = standard 1 pole MCB 32A needed. Recommend ABB or Hager but if you have another brand fitted in existing, best to follow so busbar can sit perfectly.
6. Additional busbar as necessary according to DB row where the MCB addition goes.
Only if the hob is 415V then need to modify the BOM accordingly.