 Electrical question

views
     
TSmiumiu1234
post Jul 14 2021, 06:26 PM, updated 5y ago

Getting Started
**
Junior Member
125 posts

Joined: Jun 2012
Hi all, need new socket point for aircon but i juz found out my db box slot full already.. electrician suggest me add another 8way DB box... rm 1800 (+all the wiring work for air con)..

abit over my budget, anyway to save?

This post has been edited by miumiu1234: Jul 14 2021, 06:27 PM
SUSslimey
post Jul 14 2021, 07:45 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
just loop from another socket
TSmiumiu1234
post Jul 15 2021, 12:48 AM

Getting Started
**
Junior Member
125 posts

Joined: Jun 2012
QUOTE(slimey @ Jul 14 2021, 07:45 PM)
just loop from another socket
*
wont overload?
SUSslimey
post Jul 15 2021, 08:44 AM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(miumiu1234 @ Jul 15 2021, 12:48 AM)
wont overload?
*
Why would it?

Unless you are using some special aircon or that socket ring circuit is already heavily under load constantly
mini orchard
post Jul 15 2021, 09:22 AM

10k Club
********
All Stars
14,511 posts

Joined: Sep 2017
QUOTE(miumiu1234 @ Jul 15 2021, 12:48 AM)
wont overload?
*
If that guy is qualified, he would have given advised based on safety after inspection.

Seek another opinion if you think he is over charging.
Richard
post Jul 15 2021, 05:33 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(miumiu1234 @ Jul 14 2021, 06:26 PM)
Hi all, need new socket point for aircon but i juz found out my db box slot full already.. electrician suggest me add another 8way DB box... rm 1800 (+all the wiring work for air con)..

abit over my budget, anyway to save?
*
Get the electrician to check your existing DB for the least load then transfer that load to the next lightest load..

Swap out the now spare mcb with a 20/32A rated for your new Aircon pt. and pull the new wiring..

Need to use a clamp on current meter which a competent electrician should have..

Ask the existing electrician to quote and also bring in another electrician for comparison..

Edit* Electrical guidelines req that Aircon pt. is dedicated wiring and cannot share with another Aircon or looped from another 13A SSO pt.
(The reason is due to the high starting current of aircon compressor motor thermostat control from the indoor unit)

This post has been edited by Richard: Jul 15 2021, 05:47 PM
TSmiumiu1234
post Jul 15 2021, 05:54 PM

Getting Started
**
Junior Member
125 posts

Joined: Jun 2012
QUOTE(Richard @ Jul 15 2021, 05:33 PM)
Get the electrician to check your existing DB for the least load then transfer that load to the next lightest load..

Swap out the now spare mcb with a 20/32A rated for your new Aircon  pt. and pull the new wiring..

Need to use a clamp on current meter which a competent electrician should have..

Ask the existing electrician to quote and also bring in another electrician for comparison..

Edit* Electrical guidelines req that Aircon pt. is dedicated wiring and cannot share with another Aircon or looped from another 13A SSO pt.
(The reason is due to the high starting current of aircon compressor motor thermostat control from the indoor unit)
*
ok noted, i ask will them to quote again. Thanks man~
TSmiumiu1234
post Jul 15 2021, 05:55 PM

Getting Started
**
Junior Member
125 posts

Joined: Jun 2012
QUOTE(slimey @ Jul 15 2021, 08:44 AM)
Why would it?

Unless you are using some special aircon or that socket ring circuit is already heavily under load constantly
*
ok noted. Thanks.
TSmiumiu1234
post Jul 15 2021, 05:56 PM

Getting Started
**
Junior Member
125 posts

Joined: Jun 2012
QUOTE(mini orchard @ Jul 15 2021, 09:22 AM)
If that guy is qualified, he would have given advised based on safety after inspection.

Seek another opinion if you think he is over charging.
*
I think he is.. other electrician laugh when i told them the charges.. haha.
fireballs
post Jul 15 2021, 05:57 PM

10101
*******
Senior Member
5,650 posts

Joined: Mar 2012
combine some lighting mcb. usually using 10A which is overkill
then you have free slot for 20A for aircond.
SUSslimey
post Jul 15 2021, 06:04 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(Richard @ Jul 15 2021, 05:33 PM)
Get the electrician to check your existing DB for the least load then transfer that load to the next lightest load..

Swap out the now spare mcb with a 20/32A rated for your new Aircon  pt. and pull the new wiring..

Need to use a clamp on current meter which a competent electrician should have..

Ask the existing electrician to quote and also bring in another electrician for comparison..

Edit* Electrical guidelines req that Aircon pt. is dedicated wiring and cannot share with another Aircon or looped from another 13A SSO pt.
(The reason is due to the high starting current of aircon compressor motor thermostat control from the indoor unit)
*
yes.......that's the ideal scenario.

but in real world an inverter aircond compressor is soft start. and even in non-inverter the high starting current scenario isnt that bad when the run/start capacitor is in good shape/health.
mini orchard
post Jul 15 2021, 06:08 PM

10k Club
********
All Stars
14,511 posts

Joined: Sep 2017
QUOTE(miumiu1234 @ Jul 15 2021, 05:56 PM)
I think he is.. other electrician laugh when i told them the charges.. haha.
*
Two years ago when I took over a subsale house, I change the DB box ... total labour RM230.
TSmiumiu1234
post Jul 15 2021, 11:05 PM

Getting Started
**
Junior Member
125 posts

Joined: Jun 2012
QUOTE(mini orchard @ Jul 15 2021, 06:08 PM)
Two years ago when I took over a subsale house, I change the DB box  ... total labour RM230.
*
XD.. 1800.. LOL
terrycyk1981
post Jul 16 2021, 05:55 AM

New Member
*
Junior Member
31 posts

Joined: Jun 2008


Existing how many way?
amco
post Jul 17 2021, 05:33 PM

Enthusiast
*****
Senior Member
785 posts

Joined: Jan 2003
Aiyo, just plug into normal 13A 3-pin socket will do. Normal 1hp is 4A only.

Damage = One 3-pin plug RM3 + 10 feet 3-core 2.5mm RM 40
bobowyc
post Jul 17 2021, 05:38 PM

You are who you are.
******
Senior Member
1,921 posts

Joined: Apr 2013
From: Petaling Jaya


QUOTE(miumiu1234 @ Jul 14 2021, 06:26 PM)
Hi all, need new socket point for aircon but i juz found out my db box slot full already.. electrician suggest me add another 8way DB box... rm 1800 (+all the wiring work for air con)..

abit over my budget, anyway to save?
*
Whoa. All that just for a new socket point? Can shift some wires and plug in the new one.

Currently my room only 1 socket. Using it to power my ac, 2 PCs, 1 router, 3 monitors and various chargers. So far been good. No problems at all. Sometimes I turn on all 3 also.. no problem. 😅
lyt25_1234
post Jul 29 2021, 10:47 AM

Regular
******
Senior Member
1,152 posts

Joined: Jul 2011
I have a quiz, if a power outlet does not connect the ground wire to the DB, can one connect the ground wire to any where else?

Answer is......NO!

Don't play with your life. Ground wire is for your safety if the connected device to that power outlet is faulty which leads to electrical leakage.

So play safe everyone. Life has no take two.
SUSceo684
post Jul 29 2021, 02:27 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(lyt25_1234 @ Jul 29 2021, 10:47 AM)
I have a quiz, if a power outlet does not connect the ground wire to the DB, can one connect the ground wire to any where else?

Answer is......NO!

Don't play with your life. Ground wire is for your safety if the connected device to that power outlet is faulty which leads to electrical leakage.

So play safe everyone. Life has no take two.
*
Its illegal and against the code to have 13A SSO without earth wire in the first place. tongue.gif

This post has been edited by ceo684: Jul 29 2021, 02:27 PM
lyt25_1234
post Jul 29 2021, 03:29 PM

Regular
******
Senior Member
1,152 posts

Joined: Jul 2011
QUOTE(ceo684 @ Jul 29 2021, 02:27 PM)
Its illegal and against the code to have 13A SSO without earth wire in the first place. tongue.gif
*
You know it better... smile.gif
iSean
post Jul 31 2021, 04:34 PM

iz old liao.
*******
Senior Member
4,504 posts

Joined: Jun 2011



Surahanjaya Tenaga Guide from 2008

http://ocw.ump.edu.my/pluginfile.php/11228...al%20Wiring.pdf

CODE
http://ocw.ump.edu.my/pluginfile.php/11228/mod_resource/content/1/ST%20Guidelines%20For%20Electrical%20Wiring.pdf


user posted image

 

Change to: