QUOTE(slimey @ May 17 2021, 05:01 PM)
i suggest you look for another machine.
malaysia single phase is 240v, 3 phase is 415 volt. at 60hz.
Its 50hz..
QUOTE(COOLPINK @ May 17 2021, 05:24 PM)
380v ±10% is still within 415v no?
As previously you need the supplier to confirm but usually the machine should be adjusted to our Malaysia voltage to suit..
QUOTE(KennyKB @ May 17 2021, 05:30 PM)
Shoplot is usually 60A 415V three phase supply. This machine alone will take up 60A. You need to upgrade the shoplot power to at least 100A.
For a heater the voltage difference of 380V and 415V is not critical. It will probably work. You can also get a transformer manufacturer to custom make a 415V to 380V step down transformer but it is probably unnecessary.
So the main thing to do is to get the shoplot owner to upgrade the TNB supply to 100A 3 ph.
36kW 3phase would mean 12kW/phase thus 29Amps/phase well within the current carrying capacity of a 40Amp 16mm2 cable ..
Thus if your existing is already 60A 3pole(3phase) breaker there is no need to upgrade.. which will cost a bomb to pull in new larger sized cables and breakers/switchboards..
QUOTE(COOLPINK @ May 17 2021, 05:25 PM)
TS if u die die want to use that equipment with peace of mind maybe consider get a 3 Phase 415v to 380v step down transformer to use with it.
No..
For peace of mind, talk and get confirmation from the supplier..
Most of what follows are suggestions based on opinions rather than qualified advice.. So get in touch with the supplier directly since you are an interested buyer..
Edit. Logically running a motor on a higher voltage than its rated will overload as it runs faster, hotter premature its usage while having safety issues .. ditto for a heater element..
Picture showing the electrical switch with the red box highlighting a 3phase supply means that a 3phase is compulsory for the machine.. the timers are probably for an auto trans start probably for a bigger motor..
Thus most machines have built in tapping transformer adjustments or auto regulated to suit as many countries possible voltage/freq.. you have to ask them to do the adjustment(if necessary) before shipping it to you.
This post has been edited by Richard: May 18 2021, 04:56 PM