 Voltage Power ( Please help ), How to use this machine?

views
     
a13solut3
post May 17 2021, 09:00 PM

Whiner FTW!
******
Senior Member
1,759 posts

Joined: Mar 2007
From: _|_

QUOTE(lowyat101 @ May 17 2021, 06:41 PM)
» Click to show Spoiler - click again to hide... «


but need to bear in mind, the running cost for electrical unit is much higher than gas system

ask the supplier to calculate the running cost for both, based on the local electrical and gas unit price
*
Considering the efficiency of electric vs flame burning, electricity would usually more cost saving in the long run unless he is on max all the time which is doubtful.

Even I decided to go full induction in shop after cost comparison.
Richard
post May 17 2021, 10:10 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(slimey @ May 17 2021, 05:01 PM)
i suggest you look for another machine.

malaysia single phase is 240v, 3 phase is 415 volt. at 60hz.
*
Its 50hz..

QUOTE(COOLPINK @ May 17 2021, 05:24 PM)
380v ±10% is still within 415v no?
*
As previously you need the supplier to confirm but usually the machine should be adjusted to our Malaysia voltage to suit..

QUOTE(KennyKB @ May 17 2021, 05:30 PM)
Shoplot is usually 60A 415V three phase supply. This machine alone will take up 60A. You need to upgrade the shoplot power to at least 100A.

For a heater the voltage difference of 380V and 415V is not critical. It will probably work. You can also get a transformer manufacturer to custom make a 415V to 380V step down transformer but it is probably unnecessary.

So the main thing to do is to get the shoplot owner to upgrade the TNB supply to 100A 3 ph.
*
36kW 3phase would mean 12kW/phase thus 29Amps/phase well within the current carrying capacity of a 40Amp 16mm2 cable ..

Thus if your existing is already 60A 3pole(3phase) breaker there is no need to upgrade.. which will cost a bomb to pull in new larger sized cables and breakers/switchboards..

QUOTE(COOLPINK @ May 17 2021, 05:25 PM)
TS if u die die want to use that equipment with peace of mind maybe consider get a 3 Phase 415v to 380v step down transformer to use with it.
*
No..

For peace of mind, talk and get confirmation from the supplier..


Most of what follows are suggestions based on opinions rather than qualified advice.. So get in touch with the supplier directly since you are an interested buyer..

Edit. Logically running a motor on a higher voltage than its rated will overload as it runs faster, hotter premature its usage while having safety issues .. ditto for a heater element..

Picture showing the electrical switch with the red box highlighting a 3phase supply means that a 3phase is compulsory for the machine.. the timers are probably for an auto trans start probably for a bigger motor..

Thus most machines have built in tapping transformer adjustments or auto regulated to suit as many countries possible voltage/freq.. you have to ask them to do the adjustment(if necessary) before shipping it to you.

This post has been edited by Richard: May 18 2021, 04:56 PM
SUSceo684
post May 18 2021, 01:48 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(pilot202 @ May 17 2021, 04:59 PM)
Hi all,

I'm planning to purchase a snacks frying machine but I am not very sure about this machine's performance in terms of the electricity required.

As the seller gave me the information below, may I know if I put this machine inside a shoplot, will it overpowered?

This should not be something plug and use right? Sorry I'm not very sure about this.

What kind of additional work I need to perform before turning on this machine based on the Voltage and Power required.

Kindly please help
*
Buy new machine ask the seller make it accordingly to 415V 50Hz supply.
Not plug and play as it will blow a 13A plug top to bits.
Its a fixed installation device requiring a dedicated LNE circuit from DB box.
Kytz
post May 18 2021, 02:51 PM

On my way
****
Junior Member
572 posts

Joined: Jun 2005
QUOTE(Richard @ May 17 2021, 10:10 PM)

36kW 3phase would mean 12kW/phase thus 29Amps/phase well within the current carrying capacity of a 40Amp 16mm2 cable ..

Thus if your existing is already 60A 3pole(3phase) breaker there is no need to upgrade.. which will cost a bomb to pull in new larger sized cables and breakers/switchboards..
No..


*
36kW 3 phase balanced load will give 64 Amps per phase.
The current carried per phase does not change whether you split the kW load per phase or you calculate the load as balanced 3 phase load.

You can check the calculations in this website if in doubt.

https://www.rapidtables.com/calc/electric/k...Calculator.html

Parameters are:

Current Type : AC - Three Phase
Power : 36 kW
Voltage Type : Line to line
Voltage : 380V
Power Factor : 0.85

Amps : 64 Amps

Cable size should be advised by the electrician, the cable conductors size, conductor type, insulation type, as well as the installation method dictates the current carrying capacity.
ben3003
post May 18 2021, 03:00 PM

10k Club
********
All Stars
10,859 posts

Joined: Jan 2003
From: Sarawak


This is for factory use, not for commercial use.
Richard
post May 18 2021, 05:23 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(Kytz @ May 18 2021, 02:51 PM)
36kW 3 phase balanced load will give 64 Amps per phase.
The current carried per phase does not change whether you split the kW load per phase or you calculate the load as balanced 3 phase load.

You can check the calculations in this website if in doubt.

https://www.rapidtables.com/calc/electric/k...Calculator.html

Parameters are:

Current Type : AC - Three Phase
Power : 36 kW
Voltage Type : Line to line
Voltage : 380V
Power Factor : 0.85

Amps : 64 Amps

Cable size should be advised by the electrician, the cable conductors size, conductor type, insulation type, as well as the installation method dictates the current carrying capacity.
*
Ok..

My mistake.. 36kw 3phase then doesn't equate to 12kw per phase..

Its a heater so purely resistive load pf=1.. say 415V nominal use your 380v..

Cable sized for 64amps so use 3x25mm2 + 25mm2 full size NE..
Probably better use 35mm just to be safe..

Agree?

Not plug in but as a fixed connection installation..

So find a smaller snack frying machine as this machine will cost you to have a 3ph 100Amp switchboard for your shop..

This post has been edited by Richard: May 18 2021, 05:34 PM
Kytz
post May 18 2021, 05:51 PM

On my way
****
Junior Member
572 posts

Joined: Jun 2005
QUOTE(Richard @ May 18 2021, 05:23 PM)
Ok.. 

My mistake.. 36kw 3phase then doesn't equate to 12kw per phase..

Its a heater so purely resistive load pf=1.. say 415V nominal  use your 380v..

Cable sized  for 64amps  so use 3x25mm2 + 25mm2 full size NE..
Probably better use 35mm just to be safe..

Agree?

Not plug in but as a fixed connection installation..

So find a smaller snack frying machine as this machine will cost you to have a 3ph 100Amp switchboard for your shop..
*
You were right that 36kW on 3 phase means 12 kW per phase for all 3 phases, because its a balanced 3 phase load. But calculating from 3 phase or 1 phase load should get the same current in Amps.
Also right on resistive = pf of 1 for the machine. Used p.f. = 0.85 because I'm too used to using a standard p.f.

Cables will depend on his circuit breaker size, but he will need 5 wires, 3 phase + 1 neutral and 1 earth.

Fixed connection is pretty much the way to go for these machines, best to have an isolator installed close to the machine though.

This post has been edited by Kytz: May 18 2021, 05:52 PM

 