QUOTE(clickNsnap @ Jan 16 2021, 08:05 PM)
Thanks for the advises.
You mentioned "Yes can direct replace the 0.1A (100mA) with 0.03 (30mA)"....do you means i can replace the "hager 63A/100mA that i have in my current set-up?
I was thinking to trace the maxguard MCB C16/C20 that attached to the WH, replace it with branded MCB with 10mA or 30mA....will it served the protection purpose?
Btw, i will buy the parts and ask technician to help me to replace the MCB.
Any ideals what is the different for the maxguard MCB C16 and C20?
Yes, you are right, the RCD 10mA should be installed for WH, it was regulated in 1994.... but not many people is aware of this!
Checked my WH menu, there is a built-in RCD, but no specific on the spec of the RCD, not sure if it is 30mA or 100mA?


You mentioned "Yes can direct replace the 0.1A (100mA) with 0.03 (30mA)"....do you means i can replace the "hager 63A/100mA that i have in my current set-up?
Yes, replace this with 30mA main RCD (specifically 63A 2P 30mA type)I was thinking to trace the maxguard MCB C16/C20 that attached to the WH, replace it with branded MCB with 10mA or 30mA....will it served the protection purpose? MCB and RCD operate differently (like seatbelt and reverse sensor of your car).
MCB protect against current overload (FIRE risk from cable overheating and the copper wont melt instantly but its the plastic insulation that catch on fire and so on that cause house fire).
RCD principle it operate when there is any current imbalance(whatever input current must = output current, this is normal condition. If 10A go in but 8A come out means the 2A must have got lost somewhere.. and that is what will trip RCD.. with a 10mA RCD >0.01A loss will trip. with a 30mA >0.03A loss will trip. That lost somewhere means a fault already.. whether leak here leak there leak thru human body is irrelevant..to the RCD current cannot "lost" one..same as bank teller if cash in drawer not tally with system means they need to hunt and trace every sen as any error means something wrong somewhere.
Just like seatbelt and reverse sensor both protect but they protect diff thing and operate differently, same goes to MCB vs RCD.For RCD, it constantly compare the IN - OUT current all the time and if there is more than the acceptable loss (based on RCD sensitivity 10mA 30mA etc) it will trip.
So because it need IN vs OUT (Live vs Neutral) comparison to work, the (IN) Live one is pretty easy to determine since u off the MCB 1 by 1 to trace, and the one that (when MCB off) doesnt turn on the WH, that should be the Live WH cable.
For the (OUT) Neutral, in DB box all the black wires typically connected to the common shared neutral busbar. This one is more time consuming as u need to isolate one by one each N (take out one by one) until you find the one that doesn't operate the WH, that should be the N WH cable.
Of course do a double take and mark these (L WH) and (N WH) with tape or sticker. Then plug them back in and confirm WH works now. Successfully identified the WH L and N now.
These (WH Live) and (WH Neutral) will need to be connected into the same 10mA RCD (load side).
The (power feed) L and N on the 10mA RCD Line side, can be connected to Line L busbar and N common busbar respectively.
To answer your question.. since already open up the DB might as well replace the whole strip of MCB and RCD.
The RCDs are more pricey than a whole strip of 6ka MCBs.
Adding a 10mA RCD will need two slot (2-way) more space though.Btw, i will buy the parts and ask technician to help me to replace the MCB.
I was thinking from a total overhaul POV.. since
adding each WH 10mA RCD will take 2-way more than existing (hence need DB box upgrade) - can also consolidate all the SPD everything into one box *subject to MCB wiring being long enough* - they do sell 36-way boxes (2 rows x 18way) -
https://shopee.com.my/EPS-EL02-(2-ROW-36-WA...6357.6805234786OR
minimally invasive one, trace back WH wiring (L and N), replace that existing MCB with RCBO (in situ). RCBO take care 2 jobs (MCB+RCD in one module size).
Any ideals what is the different for the maxguard MCB C16 and C20?
One trip at 16A rating, one trip at 20A rating. MCB Sizing should be based on load and cable size. Usually it should be no bigger than C20 for 2.5mm (13A socket/WH) cable, and C10 for light circuit (1.5mm) but if its dedicated light circuit putting C6 also won't harm anything (extra safety) since your lights in totality for whole house won't exceed 1000W whereby a C6 for light circuit is way more than enough already.Yes, you are right, the RCD 10mA should be installed for WH, it was regulated in 1994.... but not many people is aware of this!
Safety of electrical installation is taken too lightly in MY. Same old story, people maybe unaware, every year also come out in the news people die from WH electrocution. Even their 13A plug can be left hanging with the LNE inner wiring exposed for few cm instead of properly fixing up the plug to grip on the outer insulationChecked my WH menu, there is a built-in RCD, but no specific on the spec of the RCD, not sure if it is 30mA or 100mA?
Seems vague to me. In the diagram it shows a RCD at the DB box
Err on the safe side, this is cheaper (price of RCBO/RCD from top tier brands range from 100-170) than life insurance premium.This post has been edited by ceo684: Jan 16 2021, 10:03 PM