QUOTE(ahter12 @ Sep 28 2020, 01:33 PM)
For 1400 m³/hour like this Elba, it require at least 7" duct minimum. I'd recommend 8".
0-400 CFM: minimum duct size of 4”, recommended duct size of 6”
401-600 CFM: minimum duct size of 6”, recommended duct size of 8”
601-900 CFM: minimum duct size of 7”, recommended duct size of 8”-10”
901-1200 CFM: minimum duct size of 8”, recommended duct size of 10”-12”
1200 CFM: minimum 10” diameter duct, recommended duct size of 12”
I cannot find in the manual what is the size recommended

However, reducing the size it the worse thing you can do unfortunately
1400 m³/hour = 824 ft³/minute (CFM)