My contractor share one 32c mcb with 1hp ac, kitchen lighting,kitchen plugs, fridge and washing machine. Will it overload? Will it post issue?
Overload….Depends on the type and number of kitchen equipment you are plugging into the kitchen plugs…
It’s better to have dedicated line for heavy duty appliances. But some older houses with single phase wiring… 1MCB covers the whole kitchen…
If it’s a 32A MCB, make sure your wire quality is good. I requested for a 4mm wire (4mm for live and neutral and 2.5mm earth). My electrician mentioned that if it is a good quality wire, 2.5mm is sufficient.
Let’s see… 32A… ‘For a margin of safety, it’s best if the normal load on a circuit does not exceed 80% of the maximum (rated) load.’ That leaves us with 25.6A.
Assuming its 240V…. W/V= A
Kitchen Lighting 80W 0.3A
Fridge 400- 800W 1.7- 3.3A
1hp AC 800W 3.3A
Washing Machine (no dryer)500W 2.1A
Total= 7.4- 9A
25.6A-9A= 16.6A left…
How many kitchen plugs do you have?
Kitchen Plugs (Wattage may vary, based on my kitchen appliances)
Microwave 1000-1150W 4.8A
Mini Toaster Oven 800W 3.3A
Kettle 1850-2200W 9.2A
Portable Induction 2000W 8.3A
Stand Mixer 1500W 6.3A
Rice cooker 400W 1.7A
Slow cooker 250W 1.1A
Blender 900W 3.8A
32L Countertop Oven 1800W 7.5A
Just do the sum…. For total Amperage of the kitchen equipment
You can use
Blender, slow cooker, rice cooker and kettle simultaneously OR
Countertop oven and portable induction simultaneously….
Plus you won’t be using everything simultaneously…. Washing machine will only be on 1-2 hours a day, kettle 5mins each time… And your equipment setting might not be on max setting e.g countertop oven 250C max temperature max wattage.