Below are the followings specs of the AC and wiring.
Is it safe to use such thin wiring for AC with the distance of the wiring span about 8 m to the backdoor for the compressor and back into the room?
I'm not an Electrician. Wiring is done by Air Conditioning Installation Technicians.
The thickness of the cable is 2.5mm² they provided to me.



Updates:
Installed the Air Conditioning unit Already on 05-June.
06-June. It started to rain, and lightning comes, just realized the RCD will keep tripping and became more sensitive when lightning strikes.
Then a new discovery when I go Label each Circuit Breaker in the Electrical Box.
Found out that my new A/C is linked to another older A/C upstairs and other wiring outlets
So Basically no A/C in both rooms tonight. And turned off most of the unnecessary Electrical Appliances and try to Google Up another Electrician Tomorrow.
---------------------------------------------
Updates:
After reading Surahanjaya Tenaga Guide from 2008
http://ocw.ump.edu.my/pluginfile.php/11228...al%20Wiring.pdf
Realized that Air Conditions should have a 4 mm² wiring connected to 20A MCB
And my house RCD supposingly was a single 30/100 mA RCD by MaxGuard, but the technician swapped out to 300 mA MaxGuard

This post has been edited by iSean: Aug 6 2020, 01:35 AM
Attached thumbnail(s)
Jun 4 2019, 05:24 PM, updated 6y ago
Quote