 1hp Air Conditioning Cable Wiring Thickness?, 2.5mm² sufficient?

views
     
Cyberbullies
post Aug 11 2019, 04:32 PM

Getting Started
**
Junior Member
121 posts

Joined: Nov 2017
QUOTE(Richard @ Jun 10 2019, 09:08 AM)
Just to share,

An undersized cable will be a heater and adds a lot to your electricity bill..

On starting an induction motor draws 6 times the running amps and will damage switch contacts if not properly installed.

Thus do not only look at a motors running amps when sizing a cable or starting contact switches. It will wear out and adds to your electricity bill if done wrong.
*
Which one matters more? The cable running to the indoor unit or the cable running from indoor to outdoor?

Asking because my electrician pulled 2.5mm2 Caramay cable for use by the indoor but when the aircon installer came, they used a not well-known brand (though SIRIM approved) 2.5mm2 wire.

I compared and noticed the one the aircon installer used is thinner than the Caramay cable. Asked if they have other better cable but they said no.

Distance is around 2m from the indoor unit to the outdoor unit and it's a 2.5HP inverter aircon.

Not sure if i should be worried. Your thoughts?

This post has been edited by Cyberbullies: Aug 11 2019, 04:34 PM
Richard
post Aug 11 2019, 04:55 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(Cyberbullies @ Aug 11 2019, 04:32 PM)
Which one matters more? The cable running to the indoor unit or the cable running from indoor to outdoor?

Asking because my electrician pulled 2.5mm2 Caramay cable for use by the indoor but when the aircon installer came, they used a not well-known brand (though SIRIM approved) 2.5mm2 wire.

I compared and noticed the one the aircon installer used is thinner than the Caramay cable. Asked if they have other better cable but they said no.

Distance is around 2m from the indoor unit to the outdoor unit and it's a 2.5HP inverter aircon.

Not sure if i should be worried. Your thoughts?
*
The compressor motor does the heavier load currents amperes thus use the thicker size cable compare to the indoor fan unit.

Meaning to save money run the power cabling direct to the compressor then smaller control wires interconnect the controller board and compressor motor.

Same cabling structure as the car starter to understand i.e. direct battery to solenoid and starter motor.

This post has been edited by Richard: Aug 11 2019, 05:45 PM

 