QUOTE(fireballs @ Mar 6 2019, 01:26 PM)
what is the cable size? can the cable, fuseholder, meter handle 63A or 100A? if can, then can ask tnb for 100A instead.
the breakers and fuse is sized to protect cable and provide discrimination.
since we are on this page, kindly insist on
RCD - 100mA for light, 30mA for socket, 10mA for bathroom
add on SPD if there is risk of lightning
check your earthing
these will help to avoid unnecessary problems later.
Thanks for the info. About the incoming cable size, I can't see any marking last night as it was dark outside. But inside the DB, at the 63A MCB, it's 16mm.sq, and 10mm.sq for the 40A MCB. Is it good enough?
Ya I do see the 100mA, 30mA and 10mA RCDs inside the DBs. But haven't trace them to which MCB yet. I guess they should have followed the ST requirements on the home wiring. Will do a check later to see if they follow 100%.
BTW, is it suppose to be, 20A MCB for the aircond/water heater, and 32A MCB for the SSO?
There are also 4 SPDs (for each phase and neutral, In 20kA, Up <2.0kV) next to the incoming MCB, which I think is good enough for lightning protection?
Thanks