Melted 15A plug and socket. Any idea why?
|
|
Sep 22 2018, 10:43 PM, updated 8y ago
Show posts by this member only | Post
#1
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,222 posts Joined: Jan 2003 From: Ampang Jaya |
|
|
|
|
|
|
Sep 22 2018, 10:56 PM
Show posts by this member only | Post
#2
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,039 posts Joined: Oct 2006 |
Moisture kot?
|
|
|
Sep 22 2018, 11:20 PM
Show posts by this member only | IPv6 | Post
#3
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,083 posts Joined: Jan 2003 From: Kota Kinabalu |
Poor contact pressure between the neutral connections making electrical arching like welding. Common failure thus very important to have full contact on all connections especially high amperage devices.
|
|
|
Sep 22 2018, 11:21 PM
Show posts by this member only | Post
#4
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
6,914 posts Joined: Apr 2007 |
Arching.
Basically the neutral terminal at the plug is not tightened properly or got loose with time due to heat. |
|
|
Sep 22 2018, 11:32 PM
Show posts by this member only | Post
#5
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,222 posts Joined: Jan 2003 From: Ampang Jaya |
Thanks guys. Just checked some articles online as well and yeah, it seems that it is likely due to arcing. Have to be very careful when I replace the plug to make sure it's well fastened, and that there is no exposed wire that may lead to arcing. This could have lead to a fire.. thankfully it did not.
Will need to replace the wall socket as well.. hopefully, no nasty surprises when I open it up. This post has been edited by Par@dox: Sep 24 2018, 06:53 PM |
|
|
Sep 23 2018, 10:32 AM
Show posts by this member only | IPv6 | Post
#6
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
17,024 posts Joined: Jan 2005 |
QUOTE(Par@dox @ Sep 22 2018, 11:32 PM) Thanks guys. Just checked some articles online as well and yeah, it seems that it is likely due to arcing. Have to very careful when I replace the plug to make sure it's well fastened, and that there is no exposed wire that may lead to arcing. This could have lead to a fire.. thankfully it did not. If you frequent use the oven and Long hour, change it to industry type socket which can take higher amp. Or use terminal to secure the connection. This is the most safer way for high amp device.Will need to replace the wall socket as well.. hopefully, no nasty surprises when I open it up. |
|
|
|
|
|
Sep 23 2018, 10:57 AM
Show posts by this member only | Post
#7
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,516 posts Joined: Feb 2007 From: Uarla Umpur |
|
|
|
Sep 23 2018, 11:51 AM
Show posts by this member only | IPv6 | Post
#8
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
17,024 posts Joined: Jan 2005 |
|
|
|
Sep 23 2018, 09:41 PM
Show posts by this member only | Post
#9
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,222 posts Joined: Jan 2003 From: Ampang Jaya |
Err.. sorry, I am unfamiliar with the terms you just used.. What are industrial type sockets? DOL to switch?
|
|
|
Sep 23 2018, 09:42 PM
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,222 posts Joined: Jan 2003 From: Ampang Jaya |
After what happened, I went around shopping for a new 15A plug to replace the above MK one. Can't seem to find a decent quality one. All seemed inferior to the MK plug. Tried searching at Homepro, Ace Hardware, etc. Any idea where to buy a good quality plug?
|
|
|
Sep 23 2018, 09:55 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
9,206 posts Joined: Jun 2006 |
|
|
|
Sep 23 2018, 10:40 PM
Show posts by this member only | IPv6 | Post
#12
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
17,024 posts Joined: Jan 2005 |
QUOTE(Par@dox @ Sep 23 2018, 09:41 PM) Err.. sorry, I am unfamiliar with the terms you just used.. What are industrial type sockets? DOL to switch? The house socket have a limited current spec. In this case 15A. So how good quality it is, it still limited by the current spec.If the oven is running almost 15A, it reach the wall socket and plug limit. It still alright with short time running. But if running at 2-3hr or whole day ovening when festival time, that is what happening in the pic. That MK plug is already very good quality with that small melt area only. It is a UK brand. Here is my plug melting. Quality is much worst than the MK. ![]() This is the Schneider wall socket in the kitchen running at high current for long time. ![]() ![]() If you really want a safer longterm switching connection, DOL starter unit (direct online starter) which normally use on the aircon or water pump is better. ![]() A 32A DOL starter is more than enough. But the oven wiring is permanent screw into the unit. If you want to take the oven away, you have to unscrew the wire out. ( it is the best connection for high current device) |
|
|
Sep 23 2018, 10:43 PM
Show posts by this member only | IPv6 | Post
#13
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
9,050 posts Joined: Jan 2003 |
Oven should wire direct to circuit breaker. Don't use plug because it may use more than 15A.
|
|
|
|
|
|
Sep 23 2018, 10:47 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
5,650 posts Joined: Mar 2012 |
yes its due to arching because of improper contact between socket and plug.
solution = use a cooker switch ![]() homepro has it |
|
|
Sep 23 2018, 10:55 PM
Show posts by this member only | IPv6 | Post
#15
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
17,024 posts Joined: Jan 2005 |
|
|
|
Sep 23 2018, 10:59 PM
Show posts by this member only | IPv6 | Post
#16
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
17,024 posts Joined: Jan 2005 |
|
|
|
Sep 23 2018, 11:02 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
5,650 posts Joined: Mar 2012 |
yes. its the better solution than plug.
usually rated at 45A heavy duty |
|
|
Sep 24 2018, 12:38 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
You should use something like this - industrial plugs/sockets rated at higher amp (32A recommended) for high load
http://www.profactosolution.com.my/product...ll-Mounted.html |
|
|
Sep 24 2018, 06:34 PM
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,222 posts Joined: Jan 2003 From: Ampang Jaya |
Thanks.. learning a lot from the sharing.
|
|
|
Sep 24 2018, 06:39 PM
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,222 posts Joined: Jan 2003 From: Ampang Jaya |
QUOTE(fireballs @ Sep 23 2018, 10:47 PM) yes its due to arching because of improper contact between socket and plug. This is a neat solution, and I think the socket would fit into the hole in the wall nicely. solution = use a cooker switch ![]() homepro has it However, one problem.. how to conceal the cabling ah? The cable for the oven would be coming from inside the wall to the socket correct? |