QUOTE(beLIEve @ Aug 2 2017, 11:28 PM)
Hello World!
Has anyone tried inserting/pulling 12 or more 4mm^2 wires in a 1 inch PVC conduit? Any difficulty through the elbows?
According to US NEC (one of the many sites :
https://www.vikingelectric.com/c/BusinessPa...onduit_Fil_VES) , it's allowable to put up to 8x 10 AWG wires in a 3/4 inch PVC conduit. A 4mm^2 is slightly smaller than 11 AWG and 3/4 inch US is around 1 inch Malaysia measurements.
Thanks in advance.
Please refer to the Malaysian guidelines meaning as set by Suruhanjaya Tenaga, we are using 240V 50hz while the US NEC is using another set of voltages and frequency which may contribute to a different set of results..
- conduit require a space factor of 40%
- ducts require a space factor of 45%
Quote
"This means that not more than 45% of the space within the conduit or trunking must be occupied by cables, and involves calculating the cross-sectional area of each cable, including its insulation, for which the outside diameter must be known."
This also depends whether there are a lot of bends within the conduit run and whether the cable is a hard drawn solid conductor or stranded..
A multi strand fine cable is easily pulled while a solid core conductor of similar cross sectional area is not so easily pulled in the conduit..
Quote
"If too many cables are packed into the space available, there will be a greater increase in temperature during operation than if they were given more space."
Please follow your local authority guidelines as they have done the proper testing based on our particular voltages, frequency to our unique weather conditions done on type of material and construction..