QUOTE(Ice BabY @ Jan 16 2017, 11:53 AM)
Bro..
That person doing your wiring cannot even qualify as a skill worker.. This guy doesn't know what he is doing..
1. The pvc conduit has to be connected from back box to back box and terminated with a female adaptor between the pvc conduit to the box and screwed down inside the box so you can pull wire..
2. The black box elevation is wrong.. It's either 300mm, 1000mm or 1450mm above finish floor level ..
The original 13A switched socket outlets (white) look correct but the newly installed black boxes are definitely wrong..
3. Kitchen socket wiring is always direct from the DB and is only connected to maximum 2 nos 2x13A sockets in serial circuit and a maximum of 5 in ring circuit using 3x2.5mm2 pvc copper cable (Sirim/ST labelled)..
You better get a wireman to quote.. At the very least he can check that its safe to use ..
Edit * Get that guy to use a grinder to cut groove the width of the conduit into the cement before hacking and the finish has to be below 15mm below the finish cement plaster.
That hacked out section will be difficult to finish even by a skilled plasterer..