QUOTE(zul_4E @ Nov 2 2015, 01:54 PM)
Mind your language guys.. It is supposed to discuss and get update this platform. Better you guys have private message rather than bursting up here. Just my 2 cent.

Last Saturday night the rain was heavily pour and lightnings flashed. Suddenly the house went blackout. I went to the DB and turn back the 'kicked' fuse. It resulted my TV and Astro burnt. Later on, I went upstairs during turning up the bedroom light there was a minor explosion sound. This thing repeated in every rooms and toilets (upper floor which with plaster ceiling). It ended that only the staircase lamp the only one can function now. I suspected there was a leakage from the roof which the water sip in between the roof tiles. However, there is no watermark at the ceiling.

From the damages, I have lodged a report to SD earlier on Sunday. They supposed to come for a visit this afternoon. My concern is what is the cause of the problem? Is it the wiring? Roof leakage? Lightning arrestor failure? Grounding failure? Who should borne the damages?

Appreciate your opinion in this.

Sime Darby Properties (SARON 2)

Thanks,
Zulhelmi
*
Quite similar thing happened to me. My staircase lights burnt and upon inspection the particular MCB had tripped. 2 other downlights, one in master bedroom toilet and another in bedroom 3 also damaged. Were you watching Astro when the rain happened? My TV wasn't turned on during the rain.

If you can prove to them that water leakage via the roof has inadvertently caused the damage, I suppose you can ask them to pay for the damages.

Something sure is fishy with the wiring in Saron.. or the tiling job for the roof. My neighbor informed that his Astro installer told him that the roof tiles were all not properly sealed.

Archronicles
post Nov 2 2015, 02:38 PM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


QUOTE(zul_4E @ Nov 2 2015, 02:32 PM)
I supposed to meet them this evening.. The SD rep called me and informed they will come to pay for a visit with the M&E and contractor.
The TV & Astro was switched off. Suddenly it hit then all burnt out. If this not solve definitely it will be a repeated issue.
*
Unfortunately I'm working today but please let us know the updates. What time are you meeting them? I think I'm your neighbor just few houses away, can't be sure. I'll probably climb up the manhole later to inspect for any signs of water damage.
Archronicles
post Nov 2 2015, 02:55 PM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


QUOTE(zul_4E @ Nov 2 2015, 02:43 PM)
You are also at Jln Mahligai 4D?

I will keep update. just seeking you guys opinion. I'm very dissapointed because need to cover the cost of replacing the burnt stuff.
Hope SD can do something.
*
Yeah. Anyway I heard a very loud lightning strike during the rain while I was at home that day. Judging by the time gap between lightning and thunder, it seems really really nearby. Maybe it was a lightning strike straight to the surge arrestor? Perhaps you can ask them to check your surge arrestor as well.
Archronicles
post Nov 2 2015, 03:07 PM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


The surge arrestor has to be checked for proper grounding. It functions to divert the strike to earth, if not properly grounded it is basically useless.
Archronicles
post Nov 2 2015, 04:46 PM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


Anyone applied for Unifi already? Any news from them?
Archronicles
post Nov 2 2015, 10:52 PM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


QUOTE(wong8981 @ Nov 2 2015, 08:37 PM)
Wow , mind to share the rental ?
*
I think easily rm1000 for the entire house.
Archronicles
post Nov 2 2015, 11:02 PM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


QUOTE(pkypky @ Nov 2 2015, 05:42 PM)
yeah, same happen to my units, the water leaking on 2nd room upstair. yesterday had ask the contractor repair it.
there had 1 pc of roof tiles been exchange. not sure if the wind blow off or what.
As before it, raining doesnt have this leaking.
also, my down light was burnt out 2 units but can do exchange due warranty for 1 year.
no others cost involved.

any leaking, need to ask SD to do repair immediately, these few days have heavy rain in the evening time.
*
How did you noticed the leak? Obvious stain on the plaster ceiling or you climbed into the attic?

Archronicles
post Nov 3 2015, 12:28 PM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


QUOTE(ks1981 @ Nov 3 2015, 12:17 PM)
Thanks for the feedback. One of the reno contractor mentioned that that area is very prone to lightning strike. So have to be careful. I'm planning to install a surge protection device on the switchboard to minimize the risk.
*
Please share the SPD that you're planning to install. My electrical guy suggested BY1 Voltage Surge Suppressors by EPS. Don't know how good it is and never heard of the brand before.
Archronicles
post Nov 3 2015, 12:40 PM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


QUOTE(pkypky @ Nov 3 2015, 10:28 AM)
the leak can been saw on the plaster ceiling, you need to check it when it happen. i check when the time still raining.
Cuz after next day morning, the stain will be no obvious if not check in proper.

im not install any Astro, but how come my downlight also can burnt out? is it other neighbor hit the lighting and cause others house also affected?
*
Not sure bout this. Will check after a heavy rain. Problem is my staircase light was also affected, which I found strange. I've also not installed Astro yet.
Archronicles
post Nov 4 2015, 09:50 AM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


QUOTE(ks1981 @ Nov 3 2015, 12:37 PM)
Sure will do. Some reputable brands that you can consider either ABB or Schneider Electric.
*
Just checked the DB. Our units already came standard with ABB OVR T2 40-275 C and OVR T2 70 N C. What else could we add on to this config? A Type 1 protection?

This post has been edited by Archronicles: Nov 4 2015, 11:09 AM


Attached thumbnail(s)
Attached Image
Archronicles
post Nov 5 2015, 12:38 AM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


QUOTE(ks1981 @ Nov 4 2015, 10:51 PM)
Hi,

Yea i see there is already an SPD there......will ask other opinions later.
*
Yes however upon some research, the Type 2 SPD is not sufficient. Since our house comes with a lightning rod, the mandatory requirement is a Type 1 SPD.
Archronicles
post Nov 5 2015, 11:25 AM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


QUOTE(ks1981 @ Nov 5 2015, 09:06 AM)
Thanks for the valuable info.
*
By right the SPD Type 1 should've been installed by SD themselves. This has been overlooked by their M&E consultants and it is not right that we have to install this ourselves. Anybody interested in the subject can refer to the attachment by Schneider Pg14.

Any Nobat residents would be kind enough to share a picture of their Distribution board (DB)? I'd be interested to know if this was installed for their unit or it's "conveniently" left out as well. Nobat seem to have lightning rods as well.

This post has been edited by Archronicles: Nov 5 2015, 11:35 AM


Attached thumbnail(s)
Attached Image

Attached File(s)
Attached File  surge_protection_chapter_J.pdf ( 3.6mb ) Number of downloads: 31
Archronicles
post Nov 9 2015, 08:48 AM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


That being said, anyone having Saron's piping and electrical layout for sharing? smile.gif Makes DIY drilling works much easier.
Archronicles
post Nov 9 2015, 09:01 AM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


Anyway, I've just sent an email to Sime Darby few days ago to complain the lack of proper lightning protection and haven't got any reply till date. I hope more residents are aware of this problem and together we can get it solved:

[Quote]
It came to my attention recently that the surge & lightning protection of my Bandar Bukit Raja property (Saron 2) is insufficient as per both Malaysian & international IEC standards (Part 1 to 4 of IEC 62305). The risk is high as it involves the safety of house occupants as well as damage to costly electrical items. The number of affected residents is large, as it might involve both Saron & Nobat residents as well.

The reason why this is insufficient is due to the fact that the property was installed with a “Lightning Protection System” (LPS) which in this case is a lightning rod (external air terminal). According to IEC 62305, a Class 1/Type 1 SPD will be essential to protect against damage due to direct lightning striking the property. However only a Class 2/Type 2 SPD was installed and this is deemed unacceptable.

I’m rather disappointed that this fact was overlooked by your M&E consultant and would like to strongly request to replace the ABB Type 2 SPD with a Type 1+2 & Type 1 N SPD as suggested by ABB. Otherwise other manufacturers such as DEHN Type 1+2 DSH TT 2P 255 is also acceptable.
[/Unquote]

Full report with pictures are as attached as well as how lightning strikes could damage your house. Please give your comments.

P/S: Nobat residents if you could be so kind to share whether your DB has SPD Class 1 or Class 2 protection.


Attached File(s)
Attached File  SPD_SD_ComplainV2.pdf ( 545.42k ) Number of downloads: 95
Attached File  IEM_Seminar_2015_Snippet.pdf ( 3.37mb ) Number of downloads: 67
Archronicles
post Nov 11 2015, 08:38 AM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


QUOTE(zul_4E @ Nov 9 2015, 09:16 AM)
Good effort bro for the complaints to SD.

Found out that a number of owners starts to move in to Saron. Maybe there should be a community/platform/social media(fb/whatsapp/telegram) groups that can be developed to keep us update on the current issue.

Just my 2 cents.
*
If someone would like to voluntarily spearhead I'd be very willing to help & be part of the community group smile.gif With that maybe we could even organize to do fencing for Saron or just monthly "TT" sessions to discuss current issues.

QUOTE(caviars @ Nov 10 2015, 04:01 PM)
Thanks for the effort.

BTW much is the cost and effort needed to install Type 1 or Type 1+2 SPD.
*
The last I've checked with DEHN Type 1+2 is RM1200 including installation supervision from the seller. You'd have to engage with your own electrician to perform the actual installation. I've yet to get a quote from ABB. If you're also scouting around and have a better price please share.

Effort wise, I'd say not much. It will be just like installing a MCB I suppose, not sure how much re-wiring work would be involved. Good point, I'll ask and get back to you.
Archronicles
post Nov 11 2015, 08:52 AM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


QUOTE(tnchsg @ Nov 10 2015, 10:10 PM)
Earn 5 figure, buy affordable house, yet to say what the deal here...

Then what the deal of sharing the nobat park with saron? It's nobat park, not common to saron..thanks
*
QUOTE(achongs @ Nov 11 2015, 08:03 AM)
can u give me ur friend full address.
i want to report to SPRM.😅
investigate. how come people with 5 figure salary buy affordable house?
put him in the jail if he faking his salary.
*
Chill la bros, maybe during the 2 year waiting period for house completion his/her income went from 8k to 10k notworthy.gif Anything could've happened within 2 years. Also house could've been bought by his lower-income partner (not wife/husband) and as such wouldn't be subjected to the income cap. If you see massive reno (i.e. there's one I spotted in Saron 2, which include master bedroom extension & double storey rear extension), it could be that they got support from parents, lottery, black business etc. Who knows? wink.gif

Many loopholes.
Archronicles
post Nov 11 2015, 10:48 AM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


QUOTE(ks1981 @ Nov 11 2015, 09:50 AM)
Hi,

mind sharing the supplier contact details? would also like to get a quote from them.
*
Yeah, no problem. For DEHN: feing@wiseprocorsa.com.my

If you've got anything from other suppliers, please do share. Thanks.
Archronicles
post Nov 13 2015, 08:52 AM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


QUOTE(zul_4E @ Nov 12 2015, 09:58 AM)
I found out that there is a lot of stray dogs. Keep doing mess of the sampah and trespassing houses. Is there anything we can do?
*
I think we could contact SPCA? Haven't done it before, so I'm not sure of the procedures.

QUOTE(ks1981 @ Nov 13 2015, 08:27 AM)
Agreed...this has to be highlighted to the developer. Also those property agents are the ones who further inflicted the situation. At this point even the house is rented out a formal agreement cannot be established and therefore if anything goes wrong the owner cannot  take any legal action.

Cannot understand also the rental basically ranging around 1000-1100, monthly installment is about 1500-1600. Ada untung ka?
*
I suppose if the installment could cover the interest rate also considered good. Considering it is an extra property. House value will continue to appreciate if the area is good anyways.

QUOTE(wong8981 @ Nov 13 2015, 08:32 AM)
Hard to expect to cover 100% installment smile.gif
However if the tenant is a destroyer then owner may need to prepare another amount of money for maintenance later.
*
Agreed yawn.gif

This post has been edited by Archronicles: Nov 13 2015, 08:54 AM
Archronicles
post Nov 14 2015, 09:18 PM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


QUOTE(NoGuGuJiaO @ Nov 14 2015, 05:09 PM)
Anyone know any contractor can do plaster ceiling with good workmanship?
*
You may contact mr. Gan @ 0123180291. I just did flat plaster ceiling, so cant comment on cornice or other styles. Overall workmanship is alright
Archronicles
post Nov 15 2015, 06:21 PM

Getting Started
**
Junior Member
262 posts

Joined: Jan 2003
From: Klang


QUOTE(NoGuGuJiaO @ Nov 15 2015, 12:02 AM)
I also want to know about it. Going to install the aircond soon.
*
R22 Only. It is standard non-inverter piping. 2.5HP max for living hall, 1HP for master room.

4 Pages < 1 2 3 4 >Top
 

Change to:
| Lo-Fi Version
0.0623sec    0.31    7 queries    GZIP Disabled
Time is now: 7th December 2025 - 08:25 AM