post Aug 3 2020, 10:31 PM

10k Club
********
All Stars
13,913 posts

Joined: Sep 2017
QUOTE(royalz @ Aug 3 2020, 09:48 PM)
[attachmentid=10547992]
Any expert?  icon_question.gif
*
I wouldnt take the figures seriously. Different manufacturer different measurement methods....marketing/sales strategies.

"New' models, same components ... 'different specs' !

Regular maintenance will gives better efficiency than paper speccifications !
ceo684
post Aug 4 2020, 10:28 AM

Component Burner
********
All Stars
11,545 posts

Joined: Jan 2003
From: Klang/Subang



QUOTE(royalz @ Aug 3 2020, 09:48 PM)
[attachmentid=10547992]
Any expert?  icon_question.gif
*
Within the same brand the 9700 model would be better than the 9000 BTU one.. it is likely the 9000 one cut corner with smaller cooling coil so will affect cooling performance. Less metal = cheaper price yo
Kyusuke_FD3S
post Aug 4 2020, 03:17 PM

Casual
***
Junior Member
430 posts

Joined: Jul 2005
Is R410a piping can use for R32 aircond ?
mini orchard
post Aug 4 2020, 05:51 PM

10k Club
********
All Stars
13,913 posts

Joined: Sep 2017
QUOTE(Kyusuke_FD3S @ Aug 4 2020, 03:17 PM)
Is R410a piping can use for R32 aircond ?
*
Manufacturer/installer will require you to change.

You can continue to use but at your own risk relating to any warranty claim.
blanket84
post Aug 5 2020, 12:43 AM

Regular
******
Senior Member
1,498 posts

Joined: May 2008
QUOTE(james.6831 @ Jul 31 2020, 01:38 PM)
power or not mine..for condo installation...not including air con yet...
[attachmentid=10546691]
*
My contractor quoted me RM1290 for installation of 1.0hp inverter air conditioner inclusive of hacking, re-skim coat, and repaint to original wall colour.

All materials provided are sirim approved materials, 0.8mm thick copper pipe individually insulated with 3/4” thick insulation, insulated PVC drain pipe to nearest drain, PVC casing at external exposed area.

So, your price isn’t that bad sweat.gif
VeeJay
post Aug 5 2020, 12:55 AM

Look at all my stars!!
*******
Senior Member
3,763 posts

Joined: Aug 2005


QUOTE(royalz @ Aug 3 2020, 09:48 PM)
[attachmentid=10547992]
Any expert?  icon_question.gif
*
Nice chart there! biggrin.gif

I would go with the highest BTU and highest rating, hence you have 2 models to pick from.
ceo684
post Aug 5 2020, 02:17 PM

Component Burner
********
All Stars
11,545 posts

Joined: Jan 2003
From: Klang/Subang



QUOTE(Kyusuke_FD3S @ Aug 4 2020, 03:17 PM)
Is R410a piping can use for R32 aircond ?
*
Can but need to vacuum out all the old oil kau kau.
If old piping is R22 better to replace (pressure is higher for R410/R32)

Copper pipes
It is necessary to use seamless copper pipes and it is desirable that the amount of residual
oil is less than 40 mg/10 m. Do not use copper pipes having a collapsed, deformed or
discolored portion (especially on the interior surface). Otherwise, the expansion value or
capillary tube may become blocked with contaminants.
As an air conditioner using R32(R410A) incurs pressure higher than when using R22, it is
necessary to choose adequate materials.

Thicknesses of copper pipes used with R32(R410A) are as shown in Table1. Never use
copper pipes thinner than 0.8 mm even when it is available on the market.


Attached File  Fujitsu_Installation_Guide_R32_Refrigerant_Models.pdf ( 2.64mb ) Number of downloads: 31

Lina94
post Aug 5 2020, 03:36 PM

New Member
*
Newbie
35 posts

Joined: Mar 2018


Hi,

Based on below chart, should i go for Panasonic brand?


Attached Image
blanket84
post Aug 5 2020, 06:48 PM

Regular
******
Senior Member
1,498 posts

Joined: May 2008
QUOTE(Lina94 @ Aug 5 2020, 03:36 PM)
Hi,

Based on below chart, should i go for Panasonic brand?
Attached Image
*
Only one size?

Panasonic CS-U10VKH, I managed to find cheapest online price at 1469 this few weeks. About 2 months back cheapest price was 1339. About 6 months back cheapest price was 1240.

Where did you get the price? Online or physical shop? I am thinking to go to few physical shop and try to get the 2 months back price laugh.gif

This post has been edited by blanket84: Aug 5 2020, 06:49 PM
mini orchard
post Aug 5 2020, 06:49 PM

10k Club
********
All Stars
13,913 posts

Joined: Sep 2017
QUOTE(Lina94 @ Aug 5 2020, 03:36 PM)
Hi,

Based on below chart, should i go for Panasonic brand?
Attached Image
*
No layman will be able to measure those specs after installation. Too many variables.

Buy which brand you 'trust'.

This post has been edited by mini orchard: Aug 5 2020, 06:50 PM
SUSAsquith
post Aug 6 2020, 01:56 AM

On my way
****
Junior Member
647 posts

Joined: May 2020
QUOTE(ceo684 @ Aug 5 2020, 02:17 PM)
Can but need to vacuum out all the old oil kau kau.
If old piping is R22 better to replace (pressure is higher for R410/R32)

Copper pipes
It is necessary to use seamless copper pipes and it is desirable that the amount of residual
oil is less than 40 mg/10 m. Do not use copper pipes having a collapsed, deformed or
discolored portion (especially on the interior surface). Otherwise, the expansion value or
capillary tube may become blocked with contaminants.
As an air conditioner using R32(R410A) incurs pressure higher than when using R22, it is
necessary to choose adequate materials.

Thicknesses of copper pipes used with R32(R410A) are as shown in Table1. Never use
copper pipes thinner than 0.8 mm even when it is available on the market.


Attached File  Fujitsu_Installation_Guide_R32_Refrigerant_Models.pdf ( 2.64mb ) Number of downloads: 31

*
Do you by any chance know what are the procedures to find out if the process of vacuuming out the old oil was done properly?
mini orchard
post Aug 6 2020, 08:02 AM

10k Club
********
All Stars
13,913 posts

Joined: Sep 2017
QUOTE(Asquith @ Aug 6 2020, 01:56 AM)
Do you by any chance know what are the procedures to find out if the process of vacuuming out the old oil was done properly?
*
The best the technician does is to connect one end of the coil to the high pressured gas tank and pushed out the oil few times.

This post has been edited by mini orchard: Aug 6 2020, 08:46 AM
qzplx
post Aug 6 2020, 09:12 AM

Getting Started
**
Junior Member
137 posts

Joined: Nov 2006
From: SeriMaya Condo


QUOTE(Lina94 @ Aug 5 2020, 04:36 PM)
Hi,

Based on below chart, should i go for Panasonic brand?
Attached Image
*
Very informative:
From the table below I can see it sort based on the EER, what is EER ?
Based on the guideline on the table, should we choose the model with higher BTU ?
SUSAsquith
post Aug 6 2020, 05:38 PM

On my way
****
Junior Member
647 posts

Joined: May 2020
QUOTE(mini orchard @ Aug 6 2020, 08:02 AM)
The best the technician does is to connect one end of the coil to the high pressured gas tank and pushed out the oil few times.
*
Does that even clear out oil deposits?
mini orchard
post Aug 6 2020, 05:40 PM

10k Club
********
All Stars
13,913 posts

Joined: Sep 2017
QUOTE(Asquith @ Aug 6 2020, 05:38 PM)
Does that even clear out oil deposits?
*
Best effort.

Also depends on the length of your coil.

This post has been edited by mini orchard: Aug 6 2020, 05:42 PM
SUSAsquith
post Aug 6 2020, 05:42 PM

On my way
****
Junior Member
647 posts

Joined: May 2020
QUOTE(mini orchard @ Aug 6 2020, 05:40 PM)
Best effort.
*
Any idea if the residual oil could damage anything in a R32 compressor?
mini orchard
post Aug 6 2020, 05:44 PM

10k Club
********
All Stars
13,913 posts

Joined: Sep 2017
QUOTE(Asquith @ Aug 6 2020, 05:42 PM)
Any idea if the residual oil could damage anything in a R32 compressor?
*
Known few people done that, but never heard of any complaint.
axoloke
post Aug 10 2020, 09:36 AM

On my way
****
Senior Member
615 posts

Joined: Jan 2003
From: Pearl Of The Orient


Hi all, my living room aircond (York 1.5hp / 7 years old) has been giving issues quite frequently lately. Planning to change to another model, any model to recommend? Leaning towards Panasonic for now.

Questions :

1.) Worth to go for inverter or non-inverter?

Usage for weekdays : 5 hours per day.
Usage for weekends : Sometime up to 8 hours per day.

2.) The living room has a high ceiling so is it better to go with a 2hp unit? Using online calculators shows roughly a 1.75hp estimate.

Thanks!
mini orchard
post Aug 10 2020, 10:08 AM

10k Club
********
All Stars
13,913 posts

Joined: Sep 2017
QUOTE(axoloke @ Aug 10 2020, 09:36 AM)
Hi all, my living room aircond (York 1.5hp / 7 years old) has been giving issues quite frequently lately. Planning to change to another model, any model to recommend? Leaning towards Panasonic for now.

Questions :

1.) Worth to go for inverter or non-inverter?

Usage for weekdays : 5 hours per day.
Usage for weekends : Sometime up to 8 hours per day.

2.) The living room has a high ceiling so is it better to go with a 2hp unit? Using online calculators shows roughly a 1.75hp estimate.

Thanks!
*
Pana.

Inverter

2 hp ... better have higher than lower. Less stress on ac to cool the place.
axoloke
post Aug 10 2020, 12:38 PM

On my way
****
Senior Member
615 posts

Joined: Jan 2003
From: Pearl Of The Orient


QUOTE(mini orchard @ Aug 10 2020, 10:08 AM)
Pana.

Inverter

2 hp ... better have higher than lower. Less stress on ac to cool the place.
*
Thanks for the info. Any idea which looks better from these 2 Pana models? I can only see the Nanoe X as the main difference.

Premium Inverter R32 Air Conditioner
https://www.panasonic.com/my/consumer/air-s...s-u18vkh-1.html

X-Deluxe R32 Aero Series Air Conditioner
https://www.panasonic.com/my/consumer/air-s...xpu18wkh-1.html

631 Pages « < 450 451 452 453 454 > » Top
 

Change to:
| Lo-Fi Version
0.0184sec    0.28    6 queries    GZIP Disabled
Time is now: 28th March 2024 - 05:38 PM