QUOTE(heloooo @ May 19 2017, 10:01 PM)
1 aircond draw 3.91 Amp, and we know 2.5mm cable can safely carry current up to 15Amp, so can i install 2 aircond using same cable?
Not recommended.. At least By Suruhanjaya Tenaga regulations a motor is independently on its own circuit breaker ..Refer Electrical Accessories Chapt 6.1.ix electric motors shall be connected permanently to a 20A/30A rated circuit breaker/fuse together with an isolator, motor starter and 15A socket outlet. The motor outlet shall be Direct-On-Line type with the appliance together with the contactor, overload relay and on-off control. The circuit breaker/fuse which controls the motor circuit shall be capable of withstanding the starting current of the motor..
May 20 2017, 07:46 AM