 Aircon Discussion V3, Home Appliance

views
     
SUSceo684
post May 24 2021, 09:28 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(jutamind @ May 24 2021, 09:22 PM)
I actually changed the swing actuator twice. The second one much better but still got the swing sound.

Actually the random tak tak sound from the internal parts of the indoor unit is the killer in terms of noise
*
Hmm maybe the motor for flapper is too strong it actually goes beyond the available space thats why its skipping or flap clashing.

Then again I usually set the flap position (lock it to blow higher so not so cold) for my room aircon so I didn't realise this issue smile.gif
jutamind
post May 24 2021, 09:35 PM

Look at all my stars!!
*******
Senior Member
2,429 posts

Joined: Jul 2007
You can refer to this tak sound, check out about 1min 35 seconds. Try to maximize the volume to hear clearer. As you can see in this video, I didn't turn on the swing, so the sound is from internal part of the IDU

Air cond tak tak sound

QUOTE(ceo684 @ May 24 2021, 09:28 PM)
Hmm maybe the motor for flapper is too strong it actually goes beyond the available space thats why its skipping or flap clashing.

Then again I usually set the flap position (lock it to blow higher so not so cold) for my room aircon so I didn't realise this issue smile.gif
*
This post has been edited by jutamind: May 25 2021, 08:03 AM
lollipopkan
post May 25 2021, 02:39 AM

Enthusiast
*****
Junior Member
943 posts

Joined: Dec 2012


Any good 1.5hp inverter model recommended by sifu here?

I am contemplating between 2.

Gree LOMO I 1.5hp, with delivery and installation is RM1,599
https://shopee.com.my/(KL)-Gree-1HP-1.5HP-2...2237.2310096541

and

MSXS Midea 1.5hp, with delivery and installation is RM1,460
https://shopee.com.my/product/52358338/1734327075

Which one should I go for? Or is there better recommendation?


This post has been edited by lollipopkan: May 25 2021, 03:18 AM
SUSslimey
post May 25 2021, 07:09 AM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(jutamind @ May 24 2021, 09:35 PM)
You can refer to this tak sound, check out about 1min 35 seconds. Try to maximize the volume to hear clearer. As you can see in this video, I didn't turn on the swing, so the sound is from internal part of the IDU

Air cond tak tak sound
*
Seems like the sound from the coil itself.
Can happen just moments after the compressor kicks on. Caused by thermal contraction and flow of refrigerant. Usually known as a cracking sound.


jutamind
post May 25 2021, 08:08 AM

Look at all my stars!!
*******
Senior Member
2,429 posts

Joined: Jul 2007
In my case, the sound happened after compressor turn off especially if air cond set to Auto mode (meaning alternating between cooling and fan mode). Later on, the situation gets worse that it also happened in cooling mode as well.

Is this cracking sound common in other air conditioner? I can understand if it happens once a while but constantly through out the night is very disturbing for sleeping. Anything can do to remove/reduce this cracking sound?

QUOTE(slimey @ May 25 2021, 07:09 AM)
Seems like the sound from the coil itself.
Can happen just moments after the compressor kicks on. Caused by thermal contraction and flow of refrigerant. Usually known as a cracking sound.
*
mini orchard
post May 25 2021, 09:37 AM

10k Club
********
All Stars
14,511 posts

Joined: Sep 2017
QUOTE(jutamind @ May 25 2021, 08:08 AM)
In my case, the sound happened after compressor turn off especially if air cond set to Auto mode (meaning alternating between cooling and fan mode). Later on, the situation gets worse that it also happened in cooling mode as well.

Is this cracking sound common in other air conditioner? I can understand if it happens once a while but constantly through out the night is very disturbing for sleeping. Anything can do to remove/reduce this cracking sound?
*
Cracking sound can happen during a very hot day esp for terrace houses. It should only happen initially when the room starts to cool down and should stop thereafter.

If this happen often, the casing cover may not 'sit' correctly. Try to insert styrofoam to see it helps.
SUSslimey
post May 25 2021, 10:02 AM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(jutamind @ May 25 2021, 08:08 AM)
In my case, the sound happened after compressor turn off especially if air cond set to Auto mode (meaning alternating between cooling and fan mode). Later on, the situation gets worse that it also happened in cooling mode as well.

Is this cracking sound common in other air conditioner? I can understand if it happens once a while but constantly through out the night is very disturbing for sleeping. Anything can do to remove/reduce this cracking sound?
*
as far as i understand, auto mode is just automatically adjust the indoor unit fan speed automatically according to how much difference the room temperature and the set temperature.
mode of aircond dont matter much or at all as long as it is a mode that cools the air.

not much can do to reduce the sound........as the sound is created when there is a huge temperature difference between the coil temperature and the refrigerant temperature.

i would recommend an inverter aircond (soft start of the compressor and fine control of compressor speed to prevent start stop compressor) and improve the insulation of the cooling space to prevent cold air loss.
yujin86
post May 26 2021, 04:30 PM

Regular
******
Senior Member
1,736 posts

Joined: Dec 2006


1 unit of Panasonic 1HP XPU10WKH for rm1189 without installation is it ok?
FusionXY
post May 27 2021, 03:16 AM

LAZZIE ON VACATION
*******
Senior Member
3,834 posts

Joined: Aug 2016

Hey guys, need your help.
My Electrolux Air Conditioner displaying H3 error code.
Meaning compressor faulty? Or compressor overheat?
How to solve this?
Just happened at midnight and I will check again later. According to New MCO 3.0 SOP, is technician allow to fix and repair air conditioner at customer's house?
SUSceo684
post May 27 2021, 03:31 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(FusionXY @ May 27 2021, 03:16 AM)
Hey guys, need your help.
My Electrolux Air Conditioner displaying H3 error code.
Meaning compressor faulty? Or compressor overheat?
How to solve this?
Just happened at midnight and I will check again later. According to New MCO 3.0 SOP, is technician allow to fix and repair air conditioner at customer's house?
*
Error code: H3
Error name: Protect against compressor overload

Could be the run capacitor died. Its a quick fix if you can access the ODU safely..just open up it will be like a big beer can or two, and buy similar uF one online. Important: familiarise urself with capacitor handling procedure i.e. Discharge old one before touching.

SOP refer https://forum.lowyat.net/topic/5148398
Some highrise MO need to see paperwork for recent virus testing.
Although the test is pretty pointless (morning go test, afternoon infected, night result negative) as its historical and not realtime.

This post has been edited by ceo684: May 27 2021, 03:43 AM
SUSslimey
post May 27 2021, 08:09 AM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(FusionXY @ May 27 2021, 03:16 AM)
Hey guys, need your help.
My Electrolux Air Conditioner displaying H3 error code.
Meaning compressor faulty? Or compressor overheat?
How to solve this?
Just happened at midnight and I will check again later. According to New MCO 3.0 SOP, is technician allow to fix and repair air conditioner at customer's house?
*
Off the electric power and then turn it on again.

If the aircon can blow out cold air, off the aircon and then use a hose and spray water at the outdoor unit from the coil side, not the fan side. Spray the coils until water that exits the compressor run clean.

Good luck.

This should solve it.

This post has been edited by slimey: May 27 2021, 08:13 AM
SUSslimey
post May 27 2021, 08:13 AM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(ceo684 @ May 27 2021, 03:31 AM)
Error code: H3
Error name: Protect against compressor overload

Could be the run capacitor died. Its a quick fix if you can access the ODU safely..just open up it will be like a big beer can or two, and buy similar uF one online. Important: familiarise urself with capacitor handling procedure i.e. Discharge old one before touching.

SOP refer https://forum.lowyat.net/topic/5148398
Some highrise MO need to see paperwork for recent virus testing.
Although the test is pretty pointless (morning go test, afternoon infected, night result negative) as its historical and not realtime.
*
A dirty condenser coil is a usual suspect also. Where the dirty coil would cause increase in temperature and hence pressure due to lack of airflow to cool the refrigerant.

This increases the load on the compressor and hence increased current usage, possibly beyond the manufacturer limit which trips the overload mechanism.
mini orchard
post May 27 2021, 08:31 AM

10k Club
********
All Stars
14,511 posts

Joined: Sep 2017
QUOTE(FusionXY @ May 27 2021, 03:16 AM)
Hey guys, need your help.
My Electrolux Air Conditioner displaying H3 error code.
Meaning compressor faulty? Or compressor overheat?
How to solve this?
Just happened at midnight and I will check again later. According to New MCO 3.0 SOP, is technician allow to fix and repair air conditioner at customer's house?
*
When was the last date you did a service for the ac? In between did you clean the air filter ?

Anyhow, is time to call the technician. Refer to your jmb for the sop.
FusionXY
post May 27 2021, 11:33 AM

LAZZIE ON VACATION
*******
Senior Member
3,834 posts

Joined: Aug 2016

QUOTE(ceo684 @ May 27 2021, 03:31 AM)
Error code: H3
Error name: Protect against compressor overload

Could be the run capacitor died. Its a quick fix if you can access the ODU safely..just open up it will be like a big beer can or two, and buy similar uF one online. Important: familiarise urself with capacitor handling procedure i.e. Discharge old one before touching.

SOP refer https://forum.lowyat.net/topic/5148398
Some highrise MO need to see paperwork for recent virus testing.
Although the test is pretty pointless (morning go test, afternoon infected, night result negative) as its historical and not realtime.
*
Hello, thank you for the quick response. Is it expensive to replace the part?
The air conditioner is around 5 years now. I remembered around 2016 fix in the shoplot.
We fix in the shoplot then later transfer air conditioner to my sister's room.
Repair or replace air conditioner in this scenario? Is this error code H3 very common or rarely happens?

QUOTE(slimey @ May 27 2021, 08:09 AM)
Off the electric power and then turn it on again.

If the aircon can blow out cold air, off the aircon and then use a hose and spray water at the outdoor unit from the coil side, not the fan side. Spray the coils until water that exits the compressor run clean.

Good luck.

This should solve it.
*
Thank you for the quick response as well.
Last midnight happened this, then no cold air coming out.
Spray the water to left or right side of the ODU?
If right side not possible as the space is very narrow and it is blocked by the wall.
Just tried switching on, H3 error code still there with the operation light blinking.
I told my sister to switch the main power and check again later at 12pm.

QUOTE(mini orchard @ May 27 2021, 08:31 AM)
When was the last date you did a service for the ac? In between did you clean the air filter ?

Anyhow, is time to call the technician. Refer to your jmb for the sop.
*
Thank you for the quick response as well.
Last service date was 23rd April 2021. Normal service like without dismantle the whole unit down.
Just take out parts one by one. Clean the filter, indoor unit cover, swing blade. I guess the fan didn't clean.
I will check with my condominium management and the technician afterwards.
SUSslimey
post May 27 2021, 12:56 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(FusionXY @ May 27 2021, 11:33 AM)
Hello, thank you for the quick response. Is it expensive to replace the part?
The air conditioner is around 5 years now. I remembered around 2016 fix in the shoplot.
We fix in the shoplot then later transfer air conditioner to my sister's room.
Repair or replace air conditioner in this scenario? Is this error code H3 very common or rarely happens?
Thank you for the quick response as well.
Last midnight happened this, then no cold air coming out.
Spray the water to left or right side of the ODU?
If right side not possible as the space is very narrow and it is blocked by the wall.
Just tried switching on, H3 error code still there with the operation light blinking.
I told my sister to switch the main power and check again later at 12pm.
Thank you for the quick response as well.
Last service date was 23rd April 2021. Normal service like without dismantle the whole unit down.
Just take out parts one by one. Clean the filter, indoor unit cover, swing blade. I guess the fan didn't clean.
I will check with my condominium management and the technician afterwards.
*
Did you unplug the electricity of the aircon before switch on?


FusionXY
post May 27 2021, 01:41 PM

LAZZIE ON VACATION
*******
Senior Member
3,834 posts

Joined: Aug 2016

QUOTE(slimey @ May 27 2021, 12:56 PM)
Did you unplug the electricity of the aircon before switch on?
*
I tried many times still same. I switch off then wait for 30 minutes then power on via remote control.
First few minutes like normal then after a while H3 appears and cooling light symbol blinking.
ycs
post May 27 2021, 01:52 PM

MEMBER
*******
Senior Member
4,225 posts

Joined: Jan 2003
From: Selangor



QUOTE(FusionXY @ May 27 2021, 01:41 PM)
I tried many times still same. I switch off then wait for 30 minutes then power on via remote control.
First few minutes like normal then after a while H3 appears and cooling light symbol blinking.
*
maybe its your ODU fan not turning/rosak; initially cold air until it overheats due to fan not turning, then safety cuts off
FusionXY
post May 27 2021, 01:55 PM

LAZZIE ON VACATION
*******
Senior Member
3,834 posts

Joined: Aug 2016

QUOTE(ycs @ May 27 2021, 01:52 PM)
maybe its your ODU fan not turning/rosak; initially cold air until it overheats due to fan not turning, then safety cuts off
*
OK. Thank you for the information.
Will try to call technician first whether they are allowed to come and repair.
SUSceo684
post May 27 2021, 02:14 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(FusionXY @ May 27 2021, 01:41 PM)
I tried many times still same. I switch off then wait for 30 minutes then power on via remote control.
First few minutes like normal then after a while H3 appears and cooling light symbol blinking.
*
Make sure ODU fins are clean and clear..u can use a hose to the coils (back of AC no fan easier) wash it out. Its ODU, it can take the washing.

Sounds like run cap about 20 to 30 bux la can get a Daikin branded one online. But need to see uF rating of d old one.. buy the same uF.

This post has been edited by ceo684: May 27 2021, 02:15 PM
FusionXY
post May 27 2021, 02:29 PM

LAZZIE ON VACATION
*******
Senior Member
3,834 posts

Joined: Aug 2016

QUOTE(ceo684 @ May 27 2021, 02:14 PM)
Make sure ODU fins are clean and clear..u can use a hose to the coils (back of AC no fan easier) wash it out. Its ODU, it can take the washing.

Sounds like run cap about 20 to 30 bux la can get a Daikin branded one online. But need to see uF rating of d old one.. buy the same uF.
*
Thank you for the advice and suggestion sifu.
What if washing from the back does not help to solve the H3?
Could the compressor or capacitor problem?

This post has been edited by FusionXY: May 27 2021, 02:30 PM