QUOTE(ceo684 @ May 7 2021, 10:14 PM)
First thing to note a 1.5 is actually a 1.3 by virtue of 12k class btu vs 9k class btu of 1.0.
Your room size still got plenty of space to walk around and hold a yoga session so its not a tiny one - 1.3hp inverter will suit your use case well as it has enough capacity (12k nominal btu) and yet slow mode is around 3k btu once it gets to target temp.

Angmoh website calculator is based on their cooler ambient than ours.
*
oh,never thought of Angmoh website calculator is different rclxm9.gif
Thanks for the fast reply sis thumbsup.gif
jaychin
post May 7 2021, 11:51 PM

New Member
*
Newbie
2 posts

Joined: Sep 2016
Hi, I would like to ask if it is possible to install 1HP aircon using 2HP piping. The piping in my room is designed for 2HP, but as it is a small room, it only needs 1HP AC. Thanks.
joeblow
post May 8 2021, 12:42 AM

Regular
******
Senior Member
1,144 posts

Joined: Dec 2015


QUOTE(jaychin @ May 7 2021, 11:51 PM)
Hi, I would like to ask if it is possible to install 1HP aircon using 2HP piping. The piping in my room is designed for 2HP, but as it is a small room, it only needs 1HP AC. Thanks.
*
Yes can. I plan to do the same for my house. The reverse cannot though.
SUSceo684
post May 8 2021, 12:48 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(zsaberstar @ May 6 2021, 02:37 PM)
Hello sifus, hope to understand more about AC from you all.

I just got the keys to my condo, here is the floor plan. Ceiling height is 10ft.

user posted image

I am trying to calculate the proper size AC for my unit. Plan to install 3 units. One in Living, one in Bedroom 1 and 1 in Master Bedroom.

Currently only will have 2 occupants in Master Bedroom. Bedroom 1 will be rarely used.

I used this website to calculate:
https://airconditioner.my.panasonic.com/horsepower.html

Bedroom 1 is around 100sqft, and it just requires a 1hp. Since it will be rarely used, I plan to get a non inverter.

Master Bedroom according to my rough calculation is around 167 sqft. Using the calculator I would need a 1.5hp. and this will be frequently used >8hrs every night, so it is better to get an inverter type for energy savings.

Living Room I calculated to about 385 sqft. This will require a 3hp. This unit will most likely be turned on quite frequently so it will be a inverter type as well.

So in total I will require 1hp non inverter, 1.5hp inverter and 3hp inverter.

Is my estimation correct? Before I got the keys I showed my floor plan to an electrical store and they recommended 1hp for master bedroom and bedroom 1, and 1.5hp for living room. I am wondering why is it so different.

Thank you in advance!
*
100sf BR1 1.0hp NON (9k btu class)
this room no space to walk around after putting a double bed.
hence 9k btu enough

167sf MBR 1.3hp INV (12k btu class)
this room plenty of room to open yoga mats even with double bed installed.
QUOTE
a 9k btu works for 150sf but since this is bigger by another 10% sf,

hence 1.3hp recommended, or if wanna use 1.0hp need to look for best-in-class models with 11.5k turbo btu (9,730 nominal (2,047-11,500 turbo)) still can hack it.
for low end 1.0hp with 9k btu that maxes out their turbo mode within 9k range too, this will be insufficient (since their nominal vs turbo also no substantial difference in cooling power).

385sf LVR at least a 2.0hp INV (18k btu) minimum.. but usually 2.0 and 2.5 price delta is small so can get the 2.5hp (22k btu). A 1.3hp is confirmsure not cold.
If your place is warm (heat soak due to top floor/west facing/your target temp is low like 18C) then best to do 22k btu.
If you are like me (I can talk aircon all day but personally I can't withstand cold, the coldest I always use is just 26, typically 27C for aircon target temp) then 2.0hp will be sufficient.

QUOTE
333sf with a low end 1.3 hp (12k btu) is confirmsure insufficient. If can do 14k turbo mode (in better 1.3hp) this is barely passing.
With your 385sf a 2.0hp will be the minimum. 2.5hp if there is warming factor.


3.0hp is in extreme case like west-facing, untinted windows, zinc roof with 0 insulation, black painted walls. For 385sf a 3.0hp is likely to be grossly oversized.

QUOTE(jaychin @ May 7 2021, 11:51 PM)
Hi, I would like to ask if it is possible to install 1HP aircon using 2HP piping. The piping in my room is designed for 2HP, but as it is a small room, it only needs 1HP AC. Thanks.
*
Possible.
Actually it is also surprising that they installed 12.7+6.35mm piping when this is commonly used for 2hp (18k btu) class.
The usual size for 1.0 and 1.3hp (9k and 12k btu) is 9.52+6.35mm.
What happens in the bigger copper pipe (Gas/suction line) - the smaller pipe is the liquid line, all 6.35mm so no issue here - is that the gas does lose its velocity if oversized piping is used.
Normally nothing much will happen but the risk of gas too slow to return compressor oil is there. As the longer the piping means the gas slow down even more, if AC spec max piping length is 20m with usual size, when you run oversized gas line you need to make sure your piping is lesser than actual proper spec's max length. If its around half (say actual length is 10m for a 20m max length AC) it should still work fine. More issue happen with UNDERSIZED lines than OVERSIZED (as in your case).

There exist 1.5 hp models from Pana using the 12.7+6.35mm piping size requirement so you don't need to worry about the pipe size.
One example is 1.5HP ECONAVI Non-Inverter Deluxe Air Conditioner CS-C12QKH (CU-C12QKH)
jaychin
post May 8 2021, 09:56 AM

New Member
*
Newbie
2 posts

Joined: Sep 2016
Hello Sifus,
Not sure if this is appropriate to ask here, several AC sellers I approached told me Pana and Daikin are out of stock in the market... not sure if this is a marketing gimmick or sales push strategy. Am looking for 8 units as part of my house reno. Can anyone share/PM reliable seller contacts?
Thanks!
mini orchard
post May 8 2021, 10:03 AM

10k Club
********
All Stars
14,511 posts

Joined: Sep 2017
QUOTE(jaychin @ May 8 2021, 09:56 AM)
Hello Sifus,
Not sure if this is appropriate to ask here, several AC sellers I approached told me Pana and Daikin are out of stock in the market... not sure if this is a marketing gimmick or sales push strategy. Am looking for 8 units as part of my house reno. Can anyone share/PM reliable seller contacts?
Thanks!
*
There are no reasons for sellers to hold back stock if you agreed to their price. High stock inventory is dead money.

Buy from those authorised resellers selling pana or daikin and not from those selling mixed brands. If they still dont have stock, then is manufacturers problem.
joeblow
post May 8 2021, 05:29 PM

Regular
******
Senior Member
1,144 posts

Joined: Dec 2015


Not sure if this is the right thread to ask.

Do you guys tint your windows? Personally I will be using those blind that prevents light from coming in, but not sure if still need to tint? Effect really good?

Current house has tint but I bet it loses effectiveness already since over 20 years. Not sure if aircon good enough.

Appreciate if you guys can intro too the tint you use if indeed tint is very much a necessity. Thanks.

For aircon, yes indeed a lot of inverter aircons running out, so they say. In fact a lot of electronic stores always say this run out that run out. But when you really put money to where your mouth is, they will say get stock from their competitor etc and even give you a competitive price... lol.

For my hall (don't really know size, double storey terrace), I plan to use 2 1.5HP aircons because the in-build pipes already there and we will also install Fan. One inverter and one normal. The idea is once somewhat cool enough I will switch off the 1.5 normal one and leave only the inverter one on. Or is it I must use 2HP?

This post has been edited by joeblow: May 8 2021, 05:30 PM
mini orchard
post May 8 2021, 05:44 PM

10k Club
********
All Stars
14,511 posts

Joined: Sep 2017
QUOTE(joeblow @ May 8 2021, 05:29 PM)
Not sure if this is the right thread to ask.

Do you guys tint your windows? Personally I will be using those blind that prevents light from coming in, but not sure if still need to tint? Effect really good?

Current house has tint but I bet it loses effectiveness already since over 20 years. Not sure if aircon good enough.

Appreciate if you guys can intro too the tint you use if indeed tint is very much a necessity. Thanks.

For aircon, yes indeed a lot of inverter aircons running out, so they say. In fact a lot of electronic stores always say this run out that run out. But when you really put money to where your mouth is, they will say get stock from their competitor etc and even give you a competitive price... lol.

For my hall (don't really know size, double storey terrace), I plan to use 2 1.5HP aircons because the in-build pipes already there and we will also install Fan. One inverter and one normal. The idea is once somewhat cool enough I will switch off the 1.5 normal one and leave only the inverter one on. Or is it I must use 2HP?
*
Which half past six ac dealer will do business like you mentioned?

Most important whether buyer agreed to selling price.

If buyer willing to pay double and put the money in seller's mouth, die die also he will try to find one unit !
SUSceo684
post May 8 2021, 05:52 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(joeblow @ May 8 2021, 05:29 PM)
Not sure if this is the right thread to ask.

Do you guys tint your windows? Personally I will be using those blind that prevents light from coming in, but not sure if still need to tint? Effect really good?

Current house has tint but I bet it loses effectiveness already since over 20 years. Not sure if aircon good enough.

Appreciate if you guys can intro too the tint you use if indeed tint is very much a necessity. Thanks.


For aircon, yes indeed a lot of inverter aircons running out, so they say. In fact a lot of electronic stores always say this run out that run out. But when you really put money to where your mouth is, they will say get stock from their competitor etc and even give you a competitive price... lol.

For my hall (don't really know size, double storey terrace), I plan to use 2 1.5HP aircons because the in-build pipes already there and we will also install Fan. One inverter and one normal. The idea is once somewhat cool enough I will switch off the 1.5 normal one and leave only the inverter one on. Or is it I must use 2HP?
*
Good tint has high IRR and TSER. 3M stuff should be good, I use 3M for front windscreen only and it already cut alot of heat for the car. Rest untinted.

Darkness (visible light) transmission is not a good criteria to compare tints. Most of the heat still come in on IR which is invisible wavelength.

For your hall, best to measure the width x length in feet with measuring tape and draw out the shape in ms paint for more accurate sizing.
Because house layouts can vary, and so does the living hall..some more bedroom and small living..some no GF bedroom and long living hall.. or living room is big and have small offset for dining area.. too many possibilities. But if developer already built in the 1.3hp pipes then it may not be excessively big room.

This post has been edited by ceo684: May 8 2021, 05:54 PM
joeblow
post May 8 2021, 06:23 PM

Regular
******
Senior Member
1,144 posts

Joined: Dec 2015


QUOTE(ceo684 @ May 8 2021, 05:52 PM)
Good tint has high IRR and TSER. 3M stuff should be good, I use 3M for front windscreen only and it already cut alot of heat for the car. Rest untinted.

Darkness (visible light) transmission is not a good criteria to compare tints. Most of the heat still come in on IR which is invisible wavelength.

For your hall, best to measure the width x length in feet with measuring tape and draw out the shape in ms paint for more accurate sizing.
Because house layouts can vary, and so does the living hall..some more bedroom and small living..some no GF bedroom and long living hall.. or living room is big and have small offset for dining area.. too many possibilities. But if developer already built in the 1.3hp pipes then it may not be excessively big room.
*
Do you think a blind that blocks out light good enough to replace tint effect?

Actually the hall (need to verify) I believe they have the bigger pipes meant for 2hp. But I really don't stay in hall that long and just for dinner only. Maybe occasional guests. So I guess 2 1.5Hp should do the job. I will get the aircon guy to go see and give me recommendation.

As for the half past 6 dealer, actually it is very reputable one. But I am lazy to write again the full details, let it be. I will be buying several Panasonic 1.5hp inverter first, the rest most likely Mitsubishi non-inverter 1.5hp and 1hp. Still thinking if buy now to lock in the price or risks further price increase after 3 months (renovation period).
SUSceo684
post May 8 2021, 06:38 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(joeblow @ May 8 2021, 06:23 PM)
Do you think a blind that blocks out light good enough to replace tint effect?

Actually the hall (need to verify) I believe they have the bigger pipes meant for 2hp. But I really don't stay in hall that long and just for dinner only. Maybe occasional guests. So I guess 2 1.5Hp should do the job. I will get the aircon guy to go see and give me recommendation.

As for the half past 6 dealer, actually it is very reputable one. But I am lazy to write again the full details, let it be. I will be buying several Panasonic 1.5hp inverter first, the rest most likely Mitsubishi non-inverter 1.5hp and 1hp. Still thinking if buy now to lock in the price or risks further price increase after 3 months (renovation period).
*
If not excessively hot ie facing west then generally blinds or blackout curtains will work.

Mitsu u need to see whether it is MHI or ME. Some MHI is only 2 star ST and 1/5 yrs warranty.
Hitachi non inverter can be slightly cheaper, 3 star ST and 2/7 yrs warranty.
joeblow
post May 8 2021, 06:53 PM

Regular
******
Senior Member
1,144 posts

Joined: Dec 2015


QUOTE(ceo684 @ May 8 2021, 06:38 PM)
If not excessively hot ie facing west then generally blinds or blackout curtains will work.

Mitsu u need to see whether it is MHI or ME. Some MHI is only 2 star ST and 1/5 yrs warranty.
Hitachi non inverter can be slightly cheaper, 3 star ST and 2/7 yrs warranty.
*
Ya it is ME one, 3 stars and 2/7 years warranty made in Thailand. I am from JB area, it seems very few people carry Hitachi. Maybe I go ask around.
zsaberstar
post May 9 2021, 09:46 PM

Getting Started
**
Junior Member
66 posts

Joined: Aug 2008
From: Puchong


Thanks ceo684 for your help!

I will look to get a 1.0hp NON for bedroom 1, 1.5hp INV for Master Bedroom and 2.5hp INV for Living Room.
Created On 21/1/2021
post May 11 2021, 08:50 AM

Regular
******
Senior Member
1,347 posts

Joined: Jan 2021
QUOTE(zsaberstar @ May 9 2021, 09:46 PM)
Thanks ceo684 for your help!

I will look to get a 1.0hp NON for bedroom 1, 1.5hp INV for Master Bedroom and 2.5hp INV for Living Room.
*
Which one do you get for the 1.5HP model?
donhay
post May 11 2021, 04:19 PM

Enthusiast
*****
Junior Member
722 posts

Joined: Apr 2008
My new kondo have a 1HP aircon in living room and 1HP aircon in dining room.

I am doing renovation, want to change new aircon. Is it wise to just place one 2HP aircon in living room and cancel the dining room aircon (living room & dining room is together)

Thanks
mini orchard
post May 11 2021, 04:48 PM

10k Club
********
All Stars
14,511 posts

Joined: Sep 2017
QUOTE(donhay @ May 11 2021, 04:19 PM)
My new kondo have a 1HP aircon in living room and 1HP aircon in dining room.

I am doing renovation, want to change new aircon. Is it wise to just place one 2HP aircon in living room and cancel the dining room aircon (living room & dining room is together)

Thanks
*
No.
coolguy99
post May 11 2021, 05:25 PM

Look at all my stars!!
*******
Senior Member
7,351 posts

Joined: Aug 2015



QUOTE(donhay @ May 11 2021, 04:19 PM)
My new kondo have a 1HP aircon in living room and 1HP aircon in dining room.

I am doing renovation, want to change new aircon. Is it wise to just place one 2HP aircon in living room and cancel the dining room aircon (living room & dining room is together)

Thanks
*
No. It is still advisable to get two separate airconds.
SUSceo684
post May 11 2021, 09:02 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(donhay @ May 11 2021, 04:19 PM)
My new kondo have a 1HP aircon in living room and 1HP aircon in dining room.

I am doing renovation, want to change new aircon. Is it wise to just place one 2HP aircon in living room and cancel the dining room aircon (living room & dining room is together)

Thanks
*
Pricewise about the same but better to not put all the eggs in one basket. Usually 2 separate IDU give better air circulation.
kelissa
post May 14 2021, 03:45 PM

Getting Started
**
Junior Member
75 posts

Joined: Jan 2017
Hey all,
Is there something like a smarthome solution I could use to take control of aircond temperature? Due to WFH, we sometimes have 4 AC running during day time, but some of them always set temperature at the lowest causing the electric bill to choak up. I would like to maintain temp in between 22 to 25 celcius for some of the AC units.
SUSceo684
post May 14 2021, 03:53 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(kelissa @ May 14 2021, 03:45 PM)
Hey all,
Is there something like a smarthome solution  I could use to take control of aircond temperature? Due to WFH, we sometimes have 4 AC running during day time, but some of them always set temperature at the lowest causing the electric bill to choak up. I would like to maintain temp in between 22 to 25 celcius for some of the AC units.
*
Depending on model some can be retrofit individually (per AC) with wifi module like Daikin or Pana. The hotel room controller type may not work with split AC, most casettes should be able to accept the control signals IIRC, but usually split AC dont.

If ur using inverter then the 16C freezer is not required to keep the temp running..however if power usage is a concern 25-27C will save more.