QUOTE(kimsim @ Nov 26 2014, 07:54 PM)
Just tap from the nearest power socket as well & then change the fuse to be higher one.

That is no problem at all, but still check the wires size good enough for support Aircon or unless the devolper used slim wire code and made in china one.

Usually one don't have any issue.
*
yeaa!! i was actually considering the same thing as i remembered my parents house using a normal plug to connect to the aircond, but was told by a few electrician that i have to pull the wire from the mainbox which really confused me. Using your suggestion would definitely save me a lot of time and money.

So it is possible to extend the wire from my typical plugs as in the diagram below? there is a power plug right below those switches
user posted image

This post has been edited by aztechx: Nov 26 2014, 08:07 PM
SUSkimsim
post Nov 26 2014, 08:16 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(aztechx @ Nov 26 2014, 08:07 PM)
yeaa!! i was actually considering the same thing as i remembered my parents house using a normal plug to connect to the aircond, but was told by a few electrician that i have to pull the wire from the mainbox which really confused me. Using your suggestion would definitely save me a lot of time and money.

So it is possible to extend the wire from my typical plugs as in the diagram below? there is a power plug right below those switches
user posted image
*
There is not much an issue, my rear bedroom forgot to install power also and the Aircon man tap from the original socket for support 2x1.5hp also don't have much issue, becoz bedroom socket really never used much and sharing for fridge or water heater that is bigger issue of this, if you still worried then go for inverter aircond the original input watts very minimum, unlike non inverter for each secs used the same input watts for supply compressor runs.

Inverter got part loan meant the energy will reduce from 100% to 50% after temp. are reached.
cherroy
post Nov 26 2014, 10:17 PM

20k VIP Club
Group Icon
Staff
25,802 posts

Joined: Jan 2003
From: Penang


QUOTE(aztechx @ Nov 26 2014, 08:07 PM)
yeaa!! i was actually considering the same thing as i remembered my parents house using a normal plug to connect to the aircond, but was told by a few electrician that i have to pull the wire from the mainbox which really confused me. Using your suggestion would definitely save me a lot of time and money.

So it is possible to extend the wire from my typical plugs as in the diagram below? there is a power plug right below those switches
user posted image
*
You need to check and calculate properly the total load of the wire (if you decided to pull from one of plug point) that do not exceed the maximum ability of the wire.

QUOTE(kimsim @ Nov 26 2014, 08:16 PM)
There is not much an issue, my rear bedroom forgot to install power also and the Aircon man tap from the original socket for support 2x1.5hp also don't have much issue, becoz bedroom socket really never used much and sharing for fridge or water heater that is bigger issue of this, if you still worried then go for inverter aircond the original input watts very minimum, unlike non inverter for each secs used the same input watts for supply compressor runs.

Inverter got part loan meant the energy will reduce from 100% to 50% after temp. are reached.
*
This is ill advice.

Inverter at full blown (when start operate time), it consume the same amount with non-inverter, just ability to run at partial load in operation afterwards (when the room is cool enough), that result in saving in electricity and draw less current.

Inverter is not using less current by default.
At 100% running, inverter still consume high current.

Despite many time explanation, seems like still not getting the right understanding of inverter. doh.gif
cherroy
post Nov 26 2014, 10:26 PM

20k VIP Club
Group Icon
Staff
25,802 posts

Joined: Jan 2003
From: Penang


QUOTE(aztechx @ Nov 26 2014, 07:49 PM)
Guys, below is the photo of my condo unit and im planning to install and aircond in the hall

my mistake was not preparing the aircond point before installing the plaster ceiling which is a major headache now

user posted image
Red is where i would like to place my aircond
Blue is my mainbox

I cant put the aircond at the balcony door due to my plan to raise up the curtain all the way to the ceiling.

My question is:
1) is it possible to put my aircond there?
2) Will there be any permanent damage to my plaster ceiling after they hack it to place the cables?
3) can the air cond wiring go through that beam in the middle?
4) How much will it roughly cost for the wiring works?

Thanks
*
1) possible
2) Plaster ceiling can be "re-patched" after the job done, not much an issue.
3) No contract will want/dare to drill through a beam, so you need to round it.

You need to check properly in term of load capability of wire and your total loop of the wire, from the point that wish to pull/loop for the air-cond if decided not using directly from the DB.

As even you see is just a plug point, sometimes there is plenty of loop sharing the same supply behind that you do not see.

And also, the rating of the wire pulled original that can carry how much load (A).

Easy way to check, is off the Circuit breaker in the DB, see how many point do not have current, then already know how many loop has been applied on the single pull of wire.

SUSkimsim
post Nov 26 2014, 10:38 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(cherroy @ Nov 26 2014, 10:17 PM)
You need to check and calculate properly the total load of the wire (if you decided to pull from one of plug point) that do not exceed the maximum ability of the wire.
This is ill advice.

Inverter at full blown (when start operate time), it consume the same amount with non-inverter, just ability to run at partial load in operation afterwards (when the room is cool enough), that result in saving in electricity and draw less current.

Inverter is not using less current by default.
At 100% running, inverter still consume high current.

Despite many time explanation, seems like still not getting the right understanding of inverter.  doh.gif
*
Inverter standard preset was 25C vs non inverter 23C from the starting power draw was lesser.

Don't forget inverter is variable BTU and full detect on actual temperatures indoor & outdoor also variable speed and runs.

With compare to non inverter high power input from maximun draw..

So in day time was runing higher speed or low speed as what you set on... From non inverter you can't set to 27C these was compressor stop runs.
SUSkimsim
post Nov 26 2014, 10:43 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(cherroy @ Nov 26 2014, 10:17 PM)
You need to check and calculate properly the total load of the wire (if you decided to pull from one of plug point) that do not exceed the maximum ability of the wire.
This is ill advice.

Inverter at full blown (when start operate time), it consume the same amount with non-inverter, just ability to run at partial load in operation afterwards (when the room is cool enough), that result in saving in electricity and draw less current.

Inverter is not using less current by default.
At 100% running, inverter still consume high current.

Despite many time explanation, seems like still not getting the right understanding of inverter.   doh.gif
*
Also inverter starting was runing slow speed to maximum JET speed vs non inverter full load power.

http://qualityacs.com/FAQ.htm

This post has been edited by kimsim: Nov 26 2014, 10:55 PM
ozak
post Nov 27 2014, 10:00 AM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(kimsim @ Nov 26 2014, 10:43 PM)
Also inverter starting was runing slow speed to maximum JET speed vs non inverter full load power.

http://qualityacs.com/FAQ.htm
*
Both is still reach at maximum watt of running when require.

If you see aztechx where he place the aircon. It is in the hall + dinning area. That probably require 2HP and more. Either he install underpower 1.5Hp or correct power of 2HP, both are running at high watt. (1 longer time with less watt and 1 higher watt with short time.) Is it better for him to have separate wiring ?
SUSsupersound
post Nov 27 2014, 01:56 PM

10k Club
********
Senior Member
11,554 posts

Joined: Aug 2009
QUOTE(aztechx @ Nov 26 2014, 07:49 PM)
Guys, below is the photo of my condo unit and im planning to install and aircond in the hall

my mistake was not preparing the aircond point before installing the plaster ceiling which is a major headache now

user posted image
Red is where i would like to place my aircond
Blue is my mainbox

I cant put the aircond at the balcony door due to my plan to raise up the curtain all the way to the ceiling.

My question is:
1) is it possible to put my aircond there?
2) Will there be any permanent damage to my plaster ceiling after they hack it to place the cables?
3) can the air cond wiring go through that beam in the middle?
4) How much will it roughly cost for the wiring works?

Thanks
*
1. anywhere is possible.
2. there will be damage if they hack there, else, nothing will happen.
3. not advisable as far as possible.
4. depending on the length, works to do the job.

Anyway, your plaster ceiling are really good, on heat retention.
cherroy
post Nov 27 2014, 02:21 PM

20k VIP Club
Group Icon
Staff
25,802 posts

Joined: Jan 2003
From: Penang


QUOTE(kimsim @ Nov 26 2014, 10:38 PM)
Inverter standard preset was 25C vs non inverter 23C from the starting power draw was lesser.

Don't forget inverter is variable BTU and full detect on actual temperatures indoor & outdoor also variable speed and runs.

With compare to non inverter high power input from maximun draw..

So in day time was runing higher speed or low speed as what you set on... From non inverter you can't set to 27C these was compressor stop runs.
*
I shake head with the reply.

In term of wire consideration, you considered the maximum current draw by the appliances, as it is a very dangerous to let cable to run over its rated capacity whereby wire can get hot and burn.

Please don't spread false understanding that inverter draw less current hence can loop the wire easily as compared to non-inverter. It is an ill and dangerous advice which could cost life!

They both draw the same amount of current at full blown.

Panasonic non-inverter 1 HP CU-C9QKH
https://www.panasonic.com/my/consumer/home-...r/cs-c9qkh.html
Running current = 3.6A
Powerinput = 790W

Panasonic inverter 1HP (CU-S10PKH) https://www.panasonic.com/my/consumer/home-.../cs-s10pkh.html
Running current = 3.6A
Power input = 225-920W

York YWM10L 1HP non inverter
Total current 4.38A

York Y5WMY10JF 1HP inverter http://www.scribd.com/doc/142020182/York-Inverter-Catalog

Total current 1.63~5.06A

The inverter at full blown can draw more than non-inverter.
As you need AC need to convert to DC for inverter motor to run, there may be conversion loss as well in between.
SUSkimsim
post Nov 27 2014, 02:27 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(cherroy @ Nov 27 2014, 02:21 PM)
I shake head with the reply.

In term of wire consideration, you considered the maximum current draw by the appliances, as it is a very dangerous to let cable to run over its rated capacity whereby wire can get hot and burn.

Please don't spread false understanding that inverter draw less current hence can loop the wire easily as compared to non-inverter. It is an ill and dangerous advice which could cost life!

They both draw the same amount of current at full blown.

Panasonic non-inverter 1 HP CU-C9QKH
https://www.panasonic.com/my/consumer/home-...r/cs-c9qkh.html
Running current = 3.6A
Powerinput = 790W

Panasonic inverter 1HP (CU-S10PKH) https://www.panasonic.com/my/consumer/home-.../cs-s10pkh.html
Running current = 3.6A
Power input = 225-920W

York YWM10L 1HP non inverter
Total current 4.38A

York Y5WMY10JF 1HP inverter http://www.scribd.com/doc/142020182/York-Inverter-Catalog

Total current 1.63~5.06A

The inverter at full blown can draw more than non-inverter.
As you need AC need to convert to DC for inverter motor to run, there may be conversion loss as well in between.
*
Ok, maybe nowadays for most developer has wiring cutting cost and used china made... Then have no choice died died then to be re-wiring and end story
ale8si
post Nov 27 2014, 04:07 PM

New Member
*
Junior Member
47 posts

Joined: Jul 2013
being offered Pana and Daikin by contractor, but I am keen on ME. may need to source aircon myself. any shop with good price in klang? else which brand should I opt? thks
janson_kaniaz
post Nov 27 2014, 10:35 PM

...
*******
Senior Member
6,955 posts

Joined: Apr 2008


I plan to install 3 airconds for 3 rooms. 2 rooms with each size about 11" x 20" and living room about 22" x 30"?

Any brand and horse power recommendation ?
SUSkimsim
post Nov 27 2014, 10:38 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(janson_kaniaz @ Nov 27 2014, 10:35 PM)
I plan to install 3 airconds for 3 rooms. 2 rooms with each size about 11" x 20" and living room about 22" x 30"?

Any brand and horse power recommendation ?
*
1.5hp for 11x20" and living go for 18k or 22k btu is a minimum required icon_rolleyes.gif
janson_kaniaz
post Nov 27 2014, 10:44 PM

...
*******
Senior Member
6,955 posts

Joined: Apr 2008


QUOTE(kimsim @ Nov 27 2014, 10:38 PM)
1.5hp for 11x20" and living go for 18k or 22k btu is a minimum required  icon_rolleyes.gif
*
any brand? inverter or not? prefer save electricity thumbup.gif
SUSkimsim
post Nov 27 2014, 10:48 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(janson_kaniaz @ Nov 27 2014, 10:44 PM)
any brand? inverter or not? prefer save electricity  thumbup.gif
*
ME inverter and the rest not sure. rclxm9.gif
aztechx
post Nov 27 2014, 10:57 PM

~Aviation Freak~
*******
Senior Member
3,854 posts

Joined: Mar 2006
ok ive decided to rewire the aircond from the db box for my hall aircond. However i was quoted below from my usual contractor and was wondering if its a bit on the high side

Copper Pipe for
Aircond 1 - Hall unit as shown above
Aircond 2 - master bedroom unit with wire already jutting out of wall (i assume copper wire is not needed here?)
he quoted me RM800 for copper wire (35 ft)

Aircond point (what is this?)
RM150

was wondering if its reasonable. basically the cost above includes the wiring an repatching for the fresh new wire frmo db box. since hes quotation is based on 'agak agak' very hard to get itemized bill.

This post has been edited by aztechx: Nov 28 2014, 09:37 AM
janson_kaniaz
post Nov 28 2014, 08:02 AM

...
*******
Senior Member
6,955 posts

Joined: Apr 2008


QUOTE(kimsim @ Nov 27 2014, 10:48 PM)
ME inverter and the rest not sure.  rclxm9.gif
*
okie thanks! actually only one of my bed room is frequently using air cond. the other one is more like guest room and we don't usually switch on air cond in living room as well unless got big crowd. so i assume ME inverter for the frequently used one and how about the bedroom + livingroom?
SUSkimsim
post Nov 28 2014, 09:04 AM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(janson_kaniaz @ Nov 28 2014, 08:02 AM)
okie thanks! actually only one of my bed room is frequently using air cond. the other one is more like guest room and we don't usually switch on air cond in living room as well unless got big crowd. so i assume ME inverter for the frequently used one and how about the bedroom + livingroom?
*
Aircon can be used for longer time, just get a better one, cause you may not change it often.

Like no used Aircon can be power turn it off also.
Everything your pocket money just pay for 1 time only.

Next time got GST of the price lagi higher.

Recommend you ME is easier access to blower and clean out by own.
Also quiet don't have wave noise.
Cooling also quiet good.
DecaPix
post Nov 28 2014, 10:41 AM

5 star monkey
*******
Senior Member
3,000 posts

Joined: Aug 2008
From: PeeJay
QUOTE(cherroy @ Nov 26 2014, 10:26 PM)
1) possible
2) Plaster ceiling can be "re-patched" after the job done, not much an issue.
3) No contract will want/dare to drill through a beam, so you need to round it.

You need to check properly in term of load capability of wire and your total loop of the wire, from the point that wish to pull/loop for the air-cond if decided not using directly from the DB.

As even you see is just a plug point, sometimes there is plenty of loop sharing the same supply behind that you do not see.

And also, the rating of the wire pulled original that can carry how much load (A).

Easy way to check, is off the Circuit breaker in the DB, see how many point do not have current, then already know how many loop has been applied on the single pull of wire.
*
hehe..you see the pictures posted on this forum..
i see plenty of the contractors drill through the beam so the wire can go through shocking.gif
SUSkimsim
post Nov 28 2014, 10:46 AM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


Deleted

This post has been edited by kimsim: Nov 28 2014, 10:47 AM

104 Pages « < 17 18 19 20 21 > » Top
Topic ClosedOptions
 

Change to:
| Lo-Fi Version
0.0284sec    0.65    6 queries    GZIP Disabled
Time is now: 2nd December 2025 - 08:54 PM