What you need is another person, a 240V light bulb, a test pen.
Then 1 person stand by at the distribution box and another start testing all the plug points.
Under normal condition, when you turn on the power(normal wiring), the bulb should lighted. Once lighted, remove 1 of the wire to the earth, it should trip the ELCB. If it does not trip the ELCB, then that plug point considered failed. Need to check the internal wiring.
Not really have to lay new wiring, but for a peace of mind, any high power consumer you should lay new wire, air cond, water heater, oven is some example.
Electric Wiring Inspection @ Condo NEEDED, Need to replace obsolete wiring...
Mar 24 2014, 09:40 PM