Is water heater safe to use?
|
rylim
|
Feb 12 2020, 09:02 PM
|
Getting Started

|
QUOTE(sharethebest @ Feb 19 2017, 03:00 PM) This will be for my common bathroom installation as in the picture attached Need to hunt around for something similar 16A 10mA model.  Any idea where can I buy this box?
|
|
|
|
|
|
rylim
|
Feb 13 2020, 09:23 AM
|
Getting Started

|
QUOTE(ceo684 @ Feb 13 2020, 01:48 AM) Where are you located? Shopee got 10ma RCD [attachmentid=10426833] M using ABB 10ma 25A RCD for the 10mA leakage protection coupled with B16 MCB for the overload protection at 16A. The RCD is not meant for overload protection - for that you need a MCB. In other words you cannot have the RCD as standalone.This setup consumes 3 slots in the DIN rail. RCBOs combine this into one package (leakage protection + overload protection) into one slot single unit but it costs more. [attachmentid=10426835] At full load max heat (3300W heater) it consumes 13.77A, just under the 16A capacity of the MCB (86%). Cable is 2.5mm stiff wire installed by developer + 50cm short length of flexible 3 core Fajar Cable installed by me. Do note that you might need to use a bigger MCB if you have a >3.3kW heater (nowadays seems like quite a lot of 3.6 / 4.8kW models)Actually I'm looking for the box instead and I'm located at PJ
|
|
|
|
|