i have elcb installed beside WH switch n-th years back (refer to attached pic):
May i know whether i should replace it to RCCB with 10mA sensitivity?
Is water heater safe to use?
|
|
Jun 27 2017, 10:52 PM
Return to original view | Post
#1
|
![]() ![]()
Junior Member
61 posts Joined: Jun 2006 |
|
|
|
Jun 28 2017, 09:20 AM
Return to original view | Post
#2
|
![]() ![]()
Junior Member
61 posts Joined: Jun 2006 |
|
|
|
Jun 28 2017, 09:39 AM
Return to original view | Post
#3
|
![]() ![]()
Junior Member
61 posts Joined: Jun 2006 |
QUOTE(Richard @ Jun 28 2017, 09:28 AM) The water heater must be equipt with a 10mA RCD.. my old heater states ELCB instead.That is the current mandatory requirement set by Suruhanjaya Tenaga.. Edit.. the RCD will usually have a test button to press .. Leaking a small current to ground thus tripping out the electricity supply.. If it doesn't trip then the earth wiring is suspect or the RCD is faulty.. nothing about RCD/RCCB. |