Power Box dillema
|
TSwizard83
|
May 24 2012, 11:02 PM, updated 14y ago
|
Getting Started

|
Hi all,
I am moving into a new house soon, but i heard from some of my friends if i want to put in multiple air-cons or plug points in the house i need to change the power circuit box. How true is this and is the power circuit box going to cost more than 1k ?
Thanks in advance
|
|
|
|
|
|
JinXXX
|
May 24 2012, 11:25 PM
|
|
change more like add
if existing db not big enough can add another small one or change the whole thing to a bigger one
|
|
|
|
|
|
Life_House
|
May 25 2012, 10:16 AM
|
|
before u decide to add/ change the power box, better a reliable electrician to verify for u whether the power box is of old type or new type, and if it's capable of supporting the total electrical power usage.
some electrical devices like air-cond, microwave, water-heater would eat up quite a lot of power and if not managed carefully would cause undesirable consequences including electrical shocks, short-circuit, power-plug burned, etc etc.
|
|
|
|
|
|
teq
|
May 25 2012, 10:17 AM
|
|
my electrician changed my existing one to 26-way and charged me RM500, is that reasonable?
|
|
|
|
|
|
kelvyn
|
May 25 2012, 01:45 PM
|
|
Is there a general rule with regards to the no. of AC that can be safely connected to a MCB? Say can we connect 2 nos. AC (1HP) to one MCB (20A)?
|
|
|
|
|
|
JinXXX
|
May 25 2012, 01:49 PM
|
|
QUOTE(teq @ May 25 2012, 10:17 AM) my electrician changed my existing one to 26-way and charged me RM500, is that reasonable? existing one how big ? QUOTE(kelvyn @ May 25 2012, 01:45 PM) Is there a general rule with regards to the no. of AC that can be safely connected to a MCB? Say can we connect 2 nos. AC (1HP) to one MCB (20A)? ahh don't over the power limit ? 20a = p=vi = 4400 watts.. now days 1hp ac less than 1kwatt but also need to see how your wiring is...
|
|
|
|
|
|
ozak
|
May 25 2012, 02:14 PM
|
|
QUOTE(kelvyn @ May 25 2012, 01:45 PM) Is there a general rule with regards to the no. of AC that can be safely connected to a MCB? Say can we connect 2 nos. AC (1HP) to one MCB (20A)? General rule, 1 MCB 1 item.
|
|
|
|
|
|
SUSendau02
|
May 25 2012, 02:26 PM
|
|
1 mcb is not that exp after all
|
|
|
|
|
|
weikee
|
May 25 2012, 02:26 PM
|
|
QUOTE(Life_House @ May 25 2012, 10:16 AM) before u decide to add/ change the power box, better a reliable electrician to verify for u whether the power box is of old type or new type, and if it's capable of supporting the total electrical power usage. some electrical devices like air-cond, microwave, water-heater would eat up quite a lot of power and if not managed carefully would cause undesirable consequences including electrical shocks, short-circuit, power-plug burned, etc etc. I think TS referring db box. It does not provide power, it provide space to store mcb, timer, and fuses
|
|
|
|
|
|
kelvyn
|
May 25 2012, 02:43 PM
|
|
QUOTE(endau02 @ May 25 2012, 03:26 PM) 1 mcb is not that exp after all It's not the cost. It's more of the space available to slot in additional MCB
|
|
|
|
|
|
ozak
|
May 25 2012, 02:54 PM
|
|
QUOTE(kelvyn @ May 25 2012, 02:43 PM) It's not the cost. It's more of the space available to slot in additional MCB Create the space. Follow the electrical rule.
|
|
|
|
|
|
kelvyn
|
May 25 2012, 03:26 PM
|
|
QUOTE(ozak @ May 25 2012, 03:54 PM) Create the space. Follow the electrical rule.what does that mean?
|
|
|
|
|
|
ozak
|
May 25 2012, 03:48 PM
|
|
QUOTE(kelvyn @ May 25 2012, 03:26 PM) In electrical there is a rule to follow. We cannot any how just cincai, cheating or create our ownself of way to do. You can have many way to do it. But always play by the rule. I know some will said, see no problem many yrs still running. But once problem you already gone.  The rule create by the expertise will include the problem side when arise.
|
|
|
|
|
|
kelvyn
|
May 25 2012, 03:53 PM
|
|
QUOTE(ozak @ May 25 2012, 04:48 PM) In electrical there is a rule to follow. We cannot any how just cincai, cheating or create our ownself of way to do. You can have many way to do it. But always play by the rule. I know some will said, see no problem many yrs still running. But once problem you already gone.  The rule create by the expertise will include the problem side when arise. Noted... are you in the electrical engineering?
|
|
|
|
|
|
teq
|
May 25 2012, 04:10 PM
|
|
QUOTE(JinXXX @ May 25 2012, 01:49 PM) existing one is metal box with one row 16 or 18 slots, now plastic box with 2 rows of 13 slots = 26 slots.. normally how much is the market price for changing db box and add more mcb?
|
|
|
|
|
|
ozak
|
May 25 2012, 04:11 PM
|
|
QUOTE(kelvyn @ May 25 2012, 03:53 PM) Noted... are you in the electrical engineering? 1 of my work.
|
|
|
|
|
|
stevie8
|
May 25 2012, 04:12 PM
|
|
High power appliances need one item to one MCB, things like aircond, water heater, kettle, fridge, because especially aircond and fridge go on and off automatically because when it kick start it draw a lot of current. When you have share circuit (2 or more items to one MCB), when the powerful item on it draw so much current that the other item will lack of power for that split second. If you connect a bulb sharing with aircond you will see the light dimmed for a moment. When it goes off the access current will hit the other item. what it means your other item will break sooner than its normal life span.
On off on off is no good to share.
Aslo doesn't mean you can just change a MCB with 10A or 16A to a higher Amperage like 20A and then add an aircond to its circuit by pulling the wire parallelly from a nearby point point. This is because a 10a or 16a circuit wire that was in existance is meant for low current. By adding an aircond to the circuit you overload not the new MCB but the thin wire.
|
|
|
|
|
|
weikee
|
May 25 2012, 04:56 PM
|
|
One standard is wires come from top to bottom. So when you see your socket, anything above the socket is cable run. Don't drills
Added on May 25, 2012, 5:00 pmOf course there are looping you need to identify where the main/master source. Last time the electrician told me, nearest to the db box is master.
This post has been edited by weikee: May 25 2012, 05:00 PM
|
|
|
|
|
|
TSwizard83
|
May 26 2012, 01:53 AM
|
Getting Started

|
wow so many sifu thanks ... now slowly digesting the info..
Added on May 26, 2012, 1:54 amhow much is the market price for changing db box and add more mcb?
This post has been edited by wizard83: May 26 2012, 01:54 AM
|
|
|
|
|
|
weikee
|
May 26 2012, 08:44 AM
|
|
i can't recall, mine is part of the project. You should ask few contractor to quote than you will know what the market price.
Few hundred only i doubt you get contractor to come work.
|
|
|
|
|
|
phoenix69
|
May 26 2012, 01:25 PM
|
|
Sigh... Too cheap the contractor not interested, To expensive the customer not interested..
|
|
|
|
|
|
Limamila
|
May 26 2012, 02:05 PM
|
Getting Started

|
QUOTE(wizard83 @ May 26 2012, 01:53 AM) wow so many sifu thanks ... now slowly digesting the info.. Added on May 26, 2012, 1:54 amhow much is the market price for changing db box and add more mcb? Just want to clarify, is ELCB same as MCB? and MCCB bigger type of MCB?
|
|
|
|
|
|
JinXXX
|
May 26 2012, 02:10 PM
|
|
QUOTE(Limamila @ May 26 2012, 02:05 PM) Just want to clarify, is ELCB same as MCB? and MCCB bigger type of MCB? if im not mistaken ELCB = earth leakage cb MCD = miniature CB MCCB ? never heard before
|
|
|
|
|
|
pky
|
May 27 2012, 10:30 PM
|
|
QUOTE(JinXXX @ May 26 2012, 02:10 PM) if im not mistaken ELCB = earth leakage cb MCD = miniature CB MCCB ? never heard before  ELCB = earth leakage circuit breaker. Detects leakage to earth. Newer technology which does the equivalent job of ELCB is RCD = Residue Current Device Detects residue current between L & N. MCB = Miniature Circuit Breaker Protects circuit from over current. Handles lower fault current. MCCB = Molded Case Circuit Breaker Same as MCB but can handles higher fault current due to it arc containment design and material.
|
|
|
|
|
|
nitromx
|
May 28 2012, 09:56 AM
|
|
guys,
what is the max number of Aircond we can have in single phase
|
|
|
|
|
|
kelvyn
|
May 28 2012, 10:08 AM
|
|
i recall that one aircon installer mentioned 4-5units 1HP AC. I actually don't know how accurate is that... Maybe someone else can elaborate & confirm this...
|
|
|
|
|
|
Limamila
|
May 28 2012, 10:38 AM
|
Getting Started

|
QUOTE(pky @ May 27 2012, 10:30 PM) ELCB = earth leakage circuit breaker. Detects leakage to earth. Newer technology which does the equivalent job of ELCB is RCD = Residue Current Device Detects residue current between L & N. MCB = Miniature Circuit Breaker Protects circuit from over current. Handles lower fault current. MCCB = Molded Case Circuit Breaker Same as MCB but can handles higher fault current due to it arc containment design and material. That means we can only find MCB in the DB in common house (i.e new 2-storey terrace from developer). will there be any ELCB installed as well?
|
|
|
|
|
|
kelvyn
|
May 28 2012, 10:42 AM
|
|
I reckon ELCB and MCBs are standard components in the DB
|
|
|
|
|
|
ozak
|
May 28 2012, 10:45 AM
|
|
QUOTE(kelvyn @ May 28 2012, 10:08 AM) i recall that one aircon installer mentioned 4-5units 1HP AC. I actually don't know how accurate is that... Maybe someone else can elaborate & confirm this... 1hp = 750w x 5/pcs = 3750/240v = 15.6A. 1phase = 60A
|
|
|
|
|
|
weikee
|
May 28 2012, 11:31 AM
|
|
QUOTE(ozak @ May 28 2012, 10:45 AM) 1hp = 750w x 5/pcs = 3750/240v = 15.6A. 1phase = 60A Need to add in startup, and wastage/losses. Factor in 20% will be good, if no water heater can put 10 units too.
|
|
|
|
|
|
ozak
|
May 28 2012, 11:35 AM
|
|
QUOTE(weikee @ May 28 2012, 11:31 AM) Need to add in startup, and wastage/losses. Factor in 20% will be good, if no water heater can put 10 units too. Factor till 100% also you have more than enough.
|
|
|
|
|