Jun 10 2013, 11:11 AM
|
Newbie
7 posts Joined: May 2013 |
lingleeyen
thank you for feedback |
|
|
|
Jun 29 2013, 11:14 AM
|
Junior Member
147 posts Joined: Sep 2012 |
need your advice. if a non-inverter Aircon installed to the inverter type piping, is that ok or not ? need to worry anything.. ?
thanks |
|
Jun 29 2013, 11:21 AM
|
Junior Member
157 posts Joined: Aug 2012 |
QUOTE(!gent's @ Jun 29 2013, 11:14 AM) need your advice. if a non-inverter Aircon installed to the inverter type piping, is that ok or not ? need to worry anything.. ? I am using R22 refrigerant air conditioners on inverter type piping. So far no problem.thanks This post has been edited by *CG*: Jun 29 2013, 11:21 AM |
|
Jun 29 2013, 11:37 AM
|
Junior Member
147 posts Joined: Sep 2012 |
QUOTE(*CG* @ Jun 29 2013, 11:21 AM) okok...noted that. pheeew...relief than..another thing about the gas copper piping horizontal line, it must be heading-downwards to the Aircon unit, anyone knows / can confirm that? reason is, the contractor said my piping outlet is facing upwards to the Aircon. So, the contractor must push very hard to tilt about it. (I'm not talking about the water pipe) thanks |
|
Nov 30 2014, 01:31 AM
|
Junior Member
210 posts Joined: Apr 2010 |
So far any review or feedback if inverter air cond use with non inverter piping?
|
|
Dec 1 2014, 03:10 PM
|
Junior Member
210 posts Joined: Apr 2010 |
Anyone use inverter A/C with standard piping?
Any issue and feedback? |
|
May 20 2015, 04:30 PM
|
Senior Member
681 posts Joined: Dec 2007 |
|
|
Jul 22 2015, 12:04 PM
|
Junior Member
322 posts Joined: Dec 2007 |
|
|
|
|
Jul 22 2015, 12:09 PM
|
Senior Member
5,847 posts Joined: Nov 2010 From: Malaysia 🇲🇾 |
QUOTE(rae0724 @ May 20 2015, 04:30 PM) If gauge less than G24 or G25 copper at bend junction will be break sometime At least used G23 and above. Check here http://singapore-aircon-materials.blogspot...3/gfdg.html?m=1 |
|
Dec 9 2015, 11:42 PM
|
Senior Member
2,137 posts Joined: Oct 2015 |
Inverter and Non-Inverter use different Piping.
|
|
Apr 28 2016, 09:53 PM
|
Senior Member
1,729 posts Joined: Jan 2003 From: Penang |
i'm using 1hp normal a/c at the moment, however the room is not cold enough
Therefore im thinking of upgrading to 1.5hp But R22 A/C is difficult to find now........ Can i buy R410A (non inverter) and use back my piping?.. My piping all concealed , came with house. (5 years old). I heard need to flush the pipe and make sure it is clean.. |
|
Apr 28 2016, 11:34 PM
|
Senior Member
2,137 posts Joined: Oct 2015 |
QUOTE(dopp @ Apr 28 2016, 09:53 PM) i'm using 1hp normal a/c at the moment, however the room is not cold enough You can't use back old piping. Since different refrigerant.Therefore im thinking of upgrading to 1.5hp But R22 A/C is difficult to find now........ Can i buy R410A (non inverter) and use back my piping?.. My piping all concealed , came with house. (5 years old). I heard need to flush the pipe and make sure it is clean.. You have to remove and replace new by installer. This post has been edited by TXSim: Apr 28 2016, 11:34 PM |
|
Apr 29 2016, 05:26 PM
|
Senior Member
3,755 posts Joined: Apr 2009 From: West Malaysia |
QUOTE(dopp @ Apr 28 2016, 09:53 PM) i'm using 1hp normal a/c at the moment, however the room is not cold enough r410 piping is thicker..Therefore im thinking of upgrading to 1.5hp But R22 A/C is difficult to find now........ Can i buy R410A (non inverter) and use back my piping?.. My piping all concealed , came with house. (5 years old). I heard need to flush the pipe and make sure it is clean.. |
|
May 3 2016, 11:01 PM
|
Senior Member
1,083 posts Joined: Jan 2003 From: Kota Kinabalu |
|
|
|
|
May 3 2016, 11:03 PM
|
Senior Member
2,137 posts Joined: Oct 2015 |
QUOTE(Richard @ May 3 2016, 11:01 PM) Bad advice since you don't mention anything about why the old piping cannot use a different refrigerant.. Apa la awak!!!This is Lowyat Forum. Not a place to argue. Inverter and Non-inverter use different piping. Since Non-inverter used thin pipe. Inverter use thick pipe, as spreeee mention it. Think properly before you post. In Aircon Discussion V3. No one posted bad advice like you. You are junior member in Lowyat Forum, not senior member. Post wrong or right doesn't matter, other people will correct it. Don't think this is the place to get 100% answer. This post has been edited by TXSim: May 3 2016, 11:09 PM |
|
May 3 2016, 11:19 PM
|
Senior Member
1,083 posts Joined: Jan 2003 From: Kota Kinabalu |
QUOTE(TXSim @ May 3 2016, 11:03 PM) Apa la awak!!! Its a discussion, my brother installs aircon and (copy pasted)This is Lowyat Forum. Not a place to argue. Inverter and Non-inverter use different piping. Since Non-inverter used thin pipe. Inverter use thick pipe, as spreeee mention it. QUOTE R22 vs. R410a refrigerant R22 refrigerant: As of 2010 is no longer allowed to be used in newly-manufactured air conditioners Contributes to the depletion of the ozone layer Is less capable of absorbing and releasing heat than R410a refrigerant, making it the less efficient refrigerant Is becoming more and more expensive as its use is phased out R410a refrigerant: Is approved for use in all newly-manufactured air conditioners Does not contribute to the depletion of the ozone layer Is better at absorbing and releasing heat than R22 refrigerant, making it more efficient to use Requires the use of tougher and more durable air conditioner parts, which reduces the risk of your system overheating and breaking down What is not mentioned is R410a used in Inverter Air conditioners runs at a higher pressure than R22 thus the need for thicker copper tubes.. But the regular R22 copper tube can still withstand that higher running pressure only it doesn't have the same safety factor of not springing a leak.. I would advice save money, use back the existing conceal copper tubes with the inverter aircon.. a properly installed R22 copper tube can easily handle the pressure .. Edit* Just to add.. If you have an installer asking you to replace R22 piping it's not because there's anything wrong with the existing pipes.. My brother says the same thing to his customers all the time.. the installer (like my brother) makes more money ... like i said he installs aircon.. This post has been edited by Richard: May 3 2016, 11:40 PM |
|
Oct 11 2017, 12:01 AM
|
Senior Member
2,948 posts Joined: Jun 2007 |
QUOTE(Richard @ May 3 2016, 11:19 PM) Its a discussion, my brother installs aircon and (copy pasted) hi there, since it's 2017, mind to ask are all current aircons sold in market (inverter/non-inverter) all using R410A gases? or by chance non-inverters still using CFC gas?What is not mentioned is R410a used in Inverter Air conditioners runs at a higher pressure than R22 thus the need for thicker copper tubes.. But the regular R22 copper tube can still withstand that higher running pressure only it doesn't have the same safety factor of not springing a leak.. I would advice save money, use back the existing conceal copper tubes with the inverter aircon.. a properly installed R22 copper tube can easily handle the pressure .. Edit* Just to add.. If you have an installer asking you to replace R22 piping it's not because there's anything wrong with the existing pipes.. My brother says the same thing to his customers all the time.. the installer (like my brother) makes more money ... like i said he installs aircon.. and anyway to check current piping if they are inverter ready? non-inverter pipes they use pvc, normal metal? inverter pipes use brass? so inverter pipes should look gold/bronze color? and to figure out it's spec for R22 or R410a, we have to measure the inner diameter & thickness of the pipe (can only measure the outlet since bends are hidden). and can you tell us the recommended inner diameter & thickness for both R22 & R410A gas? can R22 run efficiently on the bigger & thicker R410A pipe? also i would assume it's safer to run smaller hp AC with R410A on R22 pipe as smaller AC have lower pressure output? This post has been edited by advocado: Oct 11 2017, 12:06 AM |
|
Dec 8 2017, 10:30 AM
|
Senior Member
871 posts Joined: Apr 2006 |
Just a question. if I want to install a non-inverter aircond using inverter piping I presume it is ok?
|
|
Dec 8 2017, 11:39 AM
|
Senior Member
2,140 posts Joined: Nov 2010 |
QUOTE(owj @ Dec 8 2017, 10:30 AM) Just a question. if I want to install a non-inverter aircond using inverter piping I presume it is ok? Short answer definitely but the issue is not inverter or non inverter but what type of gas is used in the inverter or non inverter AC.Mostly what's sold now uses R410a gas with R32 as the replacement over that. Older AC we grew up with uses freon and then R22 which was was phased out. R22 based AC are current install base in many homes but market available are now R410a and in appearing recently in small numbers R32. Turning the question around should be what pipe thickness is safe for R410a/R32 based AC. Thus, it boils down to what thickness of AC copper pipe is able to withstand the operating pressure of R410a and R32 with a high margin of safety. Thickness is stated in standard wire gauge numbers but now commonly in millimetres. Older pipes uses to be gauge 25 (0.51mm), 24 (0.56mm) or 23 (0.61mm). These are ok for R22. R410/R32 however operates at 1.6/1.7 times higher pressure than R22. The minimum thickness recommended for their use is 0.71mm or 0.76mm but now many AC manufacturers specify 0.81mm minimum. There are AC pipe manufacturers do manufacture other thickness like 0.89mm, 0.91 mm or 1.0mm and higher. There are AC like multi split systems that could require thicker like 0.9 or 1.0mm or more. They are also used in [update: VRV] or in tandem with cooling and heating that are only common in European markets. That said, follow the manufacturer specification in the installation manual. Panasonic and Fujitsu normally recommends 0.81mm pipe thickness for R410a. A good example is seen here. This post has been edited by halcyon27: Dec 9 2017, 11:38 AM |