Is it safe to use electric shower?, Safety concern... Serious Talk
Is it safe to use electric shower?, Safety concern... Serious Talk
|
|
Dec 22 2011, 02:18 PM
|
![]() ![]()
Junior Member
241 posts Joined: May 2010 From: Vinovo |
Final Destination 6
|
|
|
Dec 22 2011, 02:19 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
4,721 posts Joined: Jan 2003 |
this is not to scare you all...shit...
this is real case...i also don't know how the issue can happen la... for short term, i think i'm really gonna bath cold water.... or if need hot water...i will boil.... |
|
|
Dec 22 2011, 03:30 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,516 posts Joined: Feb 2007 From: Uarla Umpur |
the wiring okie or not ??
the earthing for the house okie ? |
|
|
Dec 22 2011, 03:32 PM
|
![]() ![]() ![]() ![]()
Senior Member
672 posts Joined: Aug 2011 |
Real men bath with ice cold water.
|
|
|
Dec 22 2011, 03:38 PM
|
![]() ![]()
Junior Member
157 posts Joined: Jul 2005 |
but early morning, when need to go to work, also shower cold water? i think will die from stroke/heart attack due to sudden temperature drop.
|
|
|
Dec 22 2011, 03:40 PM
|
![]() ![]() ![]() ![]()
Senior Member
561 posts Joined: Jun 2009 From: In a Cave |
just make sure got ELCB... then u r safe..
|
|
|
Dec 22 2011, 03:45 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,009 posts Joined: Jan 2008 From: Here To: There |
damn i scare liao... mine already use long time.. when this heater shud b change?? or is it wait to rosak then baru change..??
Added on December 22, 2011, 3:45 pm QUOTE(randyhow @ Dec 22 2011, 03:40 PM) mine got elcbThis post has been edited by pang5_kiro: Dec 22 2011, 03:45 PM |
|
|
Dec 22 2011, 05:16 PM
|
![]() ![]()
Junior Member
134 posts Joined: May 2008 |
please read the manual of all electrical appliances before you use it.
on the shower unit there's a test button. please test it at least once a month, or more frequent if you are worried. it will only take you a few seconds to do the test. just press it and the power supply to the shower will be cut off. the just reset back the safety device to continue using it. that's all |
|
|
Dec 22 2011, 05:28 PM
|
![]() ![]() ![]()
Junior Member
363 posts Joined: Dec 2006 |
Someone should contact the authorities to conduct an investigation.
Not sure this comes under which department or ministry though. There could be various causes, faulty installation, lack of an ELCB, etc. Or even sabotage. |
|
|
Dec 22 2011, 09:48 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
3,772 posts Joined: Jan 2003 |
ELCB doesnt work if the earth wire is broken or not connected so push the test button on the heater
|
|
|
Dec 22 2011, 10:12 PM
|
![]() ![]() ![]() ![]() ![]()
Senior Member
848 posts Joined: Feb 2005 From: everywhere, yet nowhere. |
water coming from the shower is droplets, not a continuous stream so if got electrocuted, possible reason is touching the control panel with wet hands and got stream of water touching electrical point
still safe imo |
|
|
Dec 22 2011, 10:18 PM
|
![]() ![]() ![]()
Junior Member
352 posts Joined: Jan 2003 From: 槟城Pg |
![]() |
|
|
Dec 22 2011, 10:22 PM
|
![]() ![]() ![]()
Junior Member
475 posts Joined: Apr 2007 |
|
|
|
Dec 23 2011, 12:03 AM
|
![]()
Newbie
0 posts Joined: Dec 2011 |
QUOTE(rcracer @ Dec 22 2011, 09:48 PM) As external expert committee to SIRIM, I would like to offer some of the life saving technical fact here, and please help spread the news and educate the public.1) The ELCB or (RCD) in the water heater can only protect if there is electrical leakage from WITHIN the water heater 2) If there is a leakage from anywhere else in the house, it is then rely on the main ELCB / RCD to trip and protect the user 3) If there is any electrical leakage within the house, and the main ELCB/RCD is not working, then almost all appliances will be electrified, including the water heater. And the water heater will likely be the last point to kill because of water, even though the leakage is not from water heater itself. In the last few cases (and most likely including this case that KEVYEOH is mentioning : - All has metal hose - All were death holding on to the shower head - All has burned hand and/or body part - All can't find fault in the water heater - All has electrified earth wire, leakage from somewhere else, kill thru water heater - Should they have Non-Conductive hose, chances are they will survive To prevent ELECTROCUTION, please do all 3 tasks below : a) Make sure the main ELCB/RCD at home's main electrical box is functioning. This can be checked by pressing the "TEST" button once a month, see if it tripped. b) Make sure the ELCB/RCD within water heater is functioning. Again, this can be checked by pressing the "TEST" button once a month, see if it tripped. c) Make sure the shower hose & the control valve connected to the water heater is off non-metallic (non-conductive material). If it is, go buy a plastic one and change it. (Many argue that even it is plastic, there are still water within the hose to conduct electricity. The fact is, water is not totally conductive, having gone thru the length of the hose with the small diameter, the current conducted is not enough to kill anymore.) Please help circulate this to all your friend and love ones to save life!!! |
|
|
Dec 23 2011, 12:06 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
9,206 posts Joined: Jun 2006 |
QUOTE(kevyeoh @ Dec 22 2011, 01:39 PM) Well, i never really give this topic much thought until today when i heard that my cousin just passed away last night due to electric shock from water heater... u can use the latest models running on low voltage DC power..I'm sure almost everyone of us must have at least 1 electric water heater in the house so I'm wondering how safe is the water heater actually? Isn't the device suppose to have some built in protection? geessh.... damn scared now.... |
|
|
Dec 23 2011, 12:09 AM
|
![]()
Newbie
0 posts Joined: Dec 2011 |
QUOTE(safer @ Dec 23 2011, 12:03 AM) As external expert committee to SIRIM, I would like to offer some of the life saving technical fact here, and please help spread the news and educate the public. Hi KEVYEOH :1) The ELCB or (RCD) in the water heater can only protect if there is electrical leakage from WITHIN the water heater 2) If there is a leakage from anywhere else in the house, it is then rely on the main ELCB / RCD to trip and protect the user 3) If there is any electrical leakage within the house, and the main ELCB/RCD is not working, then almost all appliances will be electrified, including the water heater. And the water heater will likely be the last point to kill because of water, even though the leakage is not from water heater itself. In the last few cases (and most likely including this case that KEVYEOH is mentioning : - All has metal hose - All were death holding on to the shower head - All has burned hand and/or body part - All can't find fault in the water heater - All has electrified earth wire, leakage from somewhere else, kill thru water heater - Should they have Non-Conductive hose, chances are they will survive To prevent ELECTROCUTION, please do all 3 tasks below : a) Make sure the main ELCB/RCD at home's main electrical box is functioning. This can be checked by pressing the "TEST" button once a month, see if it tripped. b) Make sure the ELCB/RCD within water heater is functioning. Again, this can be checked by pressing the "TEST" button once a month, see if it tripped. c) Make sure the shower hose & the control valve connected to the water heater is off non-metallic (non-conductive material). If it is, go buy a plastic one and change it. (Many argue that even it is plastic, there are still water within the hose to conduct electricity. The fact is, water is not totally conductive, having gone thru the length of the hose with the small diameter, the current conducted is not enough to kill anymore.) Please help circulate this to all your friend and love ones to save life!!! So sad to hear about your cousin. For study and educating the public, would you be able to provide more information, such as the photo of the water heater, and possibly investigation result? |
|
|
Dec 23 2011, 12:09 AM
|
![]() ![]()
Junior Member
100 posts Joined: Oct 2011 From: Ipoh Perak |
he must be stupid enuff to play the water with electric,i mean he sure spray on the electric parts,we know how to use properly is 100% safe.....
|
|
|
Dec 23 2011, 12:09 AM
|
![]() ![]() ![]()
Junior Member
363 posts Joined: Dec 2006 |
QUOTE(safer @ Dec 23 2011, 12:03 AM) As external expert committee to SIRIM, I would like to offer some of the life saving technical fact here, and please help spread the news and educate the public. Thanks.1) The ELCB or (RCD) in the water heater can only protect if there is electrical leakage from WITHIN the water heater 2) If there is a leakage from anywhere else in the house, it is then rely on the main ELCB / RCD to trip and protect the user 3) If there is any electrical leakage within the house, and the main ELCB/RCD is not working, then almost all appliances will be electrified, including the water heater. And the water heater will likely be the last point to kill because of water, even though the leakage is not from water heater itself. In the last few cases (and most likely including this case that KEVYEOH is mentioning : - All has metal hose - All were death holding on to the shower head - All has burned hand and/or body part - All can't find fault in the water heater - All has electrified earth wire, leakage from somewhere else, kill thru water heater - Should they have Non-Conductive hose, chances are they will survive To prevent ELECTROCUTION, please do all 3 tasks below : a) Make sure the main ELCB/RCD at home's main electrical box is functioning. This can be checked by pressing the "TEST" button once a month, see if it tripped. b) Make sure the ELCB/RCD within water heater is functioning. Again, this can be checked by pressing the "TEST" button once a month, see if it tripped. c) Make sure the shower hose & the control valve connected to the water heater is off non-metallic (non-conductive material). If it is, go buy a plastic one and change it. (Many argue that even it is plastic, there are still water within the hose to conduct electricity. The fact is, water is not totally conductive, having gone thru the length of the hose with the small diameter, the current conducted is not enough to kill anymore.) Please help circulate this to all your friend and love ones to save life!!! |
|
|
Dec 23 2011, 12:12 AM
|
![]() ![]() ![]()
Junior Member
458 posts Joined: Oct 2011 From: A Lost Planet |
|
|
|
Dec 23 2011, 12:13 AM
|
![]()
Newbie
0 posts Joined: Dec 2011 |
QUOTE(ar188 @ Dec 23 2011, 12:06 AM) This is quite misleading.First, unless it is running off battery, otherwise they will still require AC to DC conversion, which still take in AC from the mains. Therefore anything wrong inside there are possibilities of electrocution. Secondly, and MOST IMPORTANTLY, most of the electrocution cases are not leakage from the water heater, but from the external sources and KILL THRU WATER HEATER! Therefore it doesn't matter whether the water heater is powered by AC or DC. |