 7core x 2.5mm cable for gate..Sufficient?

views
     
TStiensong
post Sep 7 2011, 11:09 AM, updated 15y ago

Look at all my stars!!
*******
Senior Member
2,237 posts

Joined: Jul 2011
Hi

I just installed

a) Auto Gate point using 7 core x 2.5mm PVC/SWA/PVC cable buried underground
b) Gate Light point using 2 core x 1.5mm PVC/SWA/PVC cable buried underground
c) Door bell point using 2 core x 1.5mm PVC/SWA/PVC cable burier underground

I read some people said 11 core armored cable for the gate but mine only have 7 core...So, is it sufficient? any disadvantage or problem that I may face in the future? I have been asked the contractor about this before install but he insisted 7 core was enough...

Anyone please give some explanation?

thanks a lot~


phoenix69
post Sep 7 2011, 11:13 AM

Regular
******
Senior Member
1,836 posts

Joined: Sep 2007


From what I know.. usually you get extra cores (1-2) for in the future when any of the cores deteriorate and you can replace (no need dig up the ground again).

Why not just get a 12 core, all kaw tim, got extra left over.
TStiensong
post Sep 7 2011, 11:16 AM

Look at all my stars!!
*******
Senior Member
2,237 posts

Joined: Jul 2011
It is not money issues....and I don't know why contractor don't want to install more core for me (more money to earn but they don't want)..

now, I am worried I may face problems in the future because of this....scared....haiz


Added on September 7, 2011, 11:17 ammay I know Autogate system usually required how many core?

This post has been edited by tiensong: Sep 7 2011, 11:17 AM
Jo_da48
post Sep 7 2011, 11:24 AM

Regular
******
Senior Member
1,529 posts

Joined: Feb 2011
From: PJ


If Look at you description, you are using 11 (7+2+2) core rights?

TStiensong
post Sep 7 2011, 11:29 AM

Look at all my stars!!
*******
Senior Member
2,237 posts

Joined: Jul 2011
QUOTE(Jo_da48 @ Sep 7 2011, 11:24 AM)
If Look at you description, you are using 11 (7+2+2) core rights?
*
Can be added up like that? I don't know...I thought gate itself should have 11 core?


phoenix69
post Sep 7 2011, 11:42 AM

Regular
******
Senior Member
1,836 posts

Joined: Sep 2007


If I remember right, for a normal set up 7 cores can kaw thim all the autogate + doorbell + lights. - no balance , all used up.
My contractor installing 9 cores (2 extra balance)

Maybe they want to sell you all the balance core they have in stock tongue.gif




weikee
post Sep 7 2011, 12:18 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
I don't know how 7 core can use for all gate, bell and light. Unless the light control are build on the autogate controller.

From my calculation you need 11 cores:-

Power = 3 Cores (L,N, & E)
Autogate Switch = 4 Cores (for 2 switch), some use 3 cores
Bell = 2 Cores
Light = 2 Cores

So you use up all 11, maybe 10

TStiensong
post Sep 7 2011, 12:22 PM

Look at all my stars!!
*******
Senior Member
2,237 posts

Joined: Jul 2011
ooh...according to the description of my quotation, bell, light and gate are separated...if all add up, mine one should be 11 core...


phoenix69
post Sep 7 2011, 12:44 PM

Regular
******
Senior Member
1,836 posts

Joined: Sep 2007


biggrin.gif Ahhh ... now its clear.. weikee you da man
TStiensong
post Sep 7 2011, 12:57 PM

Look at all my stars!!
*******
Senior Member
2,237 posts

Joined: Jul 2011
for me, renovation is a nightmare...If something doesn't done right, will end up a lot of problems..headache man...




phoenix69
post Sep 7 2011, 12:58 PM

Regular
******
Senior Member
1,836 posts

Joined: Sep 2007


Its fun at the same time biggrin.gif
You are building your own LEGO castle. rclxms.gif
weikee
post Sep 7 2011, 01:03 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(tiensong @ Sep 7 2011, 12:57 PM)
for me, renovation is a nightmare...If something doesn't done right, will end up a lot of problems..headache man...
*
Nothing is perfect at first time. So correction / corrective action will always happen.
Jo_da48
post Sep 7 2011, 02:19 PM

Regular
******
Senior Member
1,529 posts

Joined: Feb 2011
From: PJ


QUOTE(tiensong @ Sep 7 2011, 12:57 PM)
for me, renovation is a nightmare...If something doesn't done right, will end up a lot of problems..headache man...
*
talk about it...

orientaliew
post Sep 7 2011, 06:13 PM

Casual
***
Junior Member
331 posts

Joined: May 2009
QUOTE(tiensong @ Sep 7 2011, 12:57 PM)
for me, renovation is a nightmare...If something doesn't done right, will end up a lot of problems..headache man...
*
share with us so we can avoid the same mistake. biggrin.gif
skng03
post Sep 7 2011, 09:56 PM

Regular
******
Senior Member
1,450 posts

Joined: Oct 2008


QUOTE(weikee @ Sep 7 2011, 12:18 PM)
I don't know how 7 core can use for all gate, bell and light. Unless the light control are build on the autogate controller.

From my calculation you need 11 cores:-

Power = 3 Cores (L,N, & E)
Autogate Switch = 4 Cores (for 2 switch), some use 3 cores
Bell = 2 Cores
Light = 2 Cores

So you use up all 11, maybe 10
*
the minimum as below:

Power = 2 Cores (L,N)
the steel wire inside the 1st pvc skin = (E)

from WIKI: Armour: Steel wire armour provides mechanical protection, which means the cable can withstand higher stresses, be buried directly and used in external or underground projects.[4] The armouring is normally connected to earth and can also be used as the circuit protective conductor ("earth wire") for the equipment supplied by cable.

Autogate Switch = 3 Cores (for 2 switch)
Bell = 2 Cores
Light = 1 Cores (L only, N & E share with auto gate power)
total 8 cores


for 7 cores, the auto gate the lights on/ off control by the auto gate control panel.

7 cores = +- rm9.50/M
11 cores =+-rm15/M

go for 11 cores so that can have some spare, the cable wont cost much for link house 10m is more than enough whistling.gif


weikee
post Sep 7 2011, 10:42 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(skng03 @ Sep 7 2011, 09:56 PM)
the minimum as below:

Power = 2 Cores (L,N)
the steel wire inside the 1st pvc skin  =  (E)

from WIKI: Armour: Steel wire armour provides mechanical protection, which means the cable can withstand higher stresses, be buried directly and used in external or underground projects.[4] The armouring is normally connected to earth and can also be used as the circuit protective conductor ("earth wire") for the equipment supplied by cable.

Autogate Switch = 3 Cores (for 2 switch)
Bell = 2 Cores
Light = 1 Cores (L only, N & E share with auto gate power)
total 8 cores
for 7 cores, the auto gate the lights on/ off control by the auto gate control panel.

7 cores = +- rm9.50/M
11 cores =+-rm15/M

go for 11 cores so that can have some spare, the cable wont cost much for link house 10m is more than enough whistling.gif
*
The Steel protective usually is not grounded, unless the wireman do it. Also it usually cut out on the switch panel / faceplate.

This post has been edited by weikee: Sep 7 2011, 10:43 PM
feeroz
post Sep 8 2011, 10:18 AM

New Member
*
Junior Member
8 posts

Joined: Feb 2006
QUOTE(tiensong @ Sep 7 2011, 11:09 AM)
Hi

I just installed

a) Auto Gate point using 7 core x 2.5mm PVC/SWA/PVC cable buried underground
b) Gate Light point using 2 core x 1.5mm PVC/SWA/PVC cable buried underground
c) Door bell point using 2 core x 1.5mm PVC/SWA/PVC cable burier underground

I read some people said 11 core armored cable for the gate but mine only have 7 core...So, is it sufficient? any disadvantage or problem that I may face in the future? I have been asked the contractor about this before install but he insisted 7 core was enough...

Anyone please give some explanation?

thanks a lot~
*
Hi,

I'm about to do this too. Can I know how much roughly is the cost.

TQ
TStiensong
post Sep 8 2011, 10:29 AM

Look at all my stars!!
*******
Senior Member
2,237 posts

Joined: Jul 2011
a) Auto Gate point using 7 core x 2.5mm PVC/SWA/PVC cable buried underground RM450 (per nos)
b) Gate Light point using 2 core x 1.5mm PVC/SWA/PVC cable buried underground RM120 (per nos)
c) Door bell point using 2 core x 1.5mm PVC/SWA/PVC cable burier underground RM120 (per nos)
kamion
post Sep 8 2011, 12:55 PM

Casual
***
Junior Member
327 posts

Joined: Feb 2011
Question, so if the electrician run a single 7 core cable, and can do everything, then the electrician shouldn't charge separately for each type: autogate, bell and gate lights?


TStiensong
post Sep 8 2011, 02:14 PM

Look at all my stars!!
*******
Senior Member
2,237 posts

Joined: Jul 2011
Hmm..based on few quotations that I received, all charge separately....


feeroz
post Sep 8 2011, 02:54 PM

New Member
*
Junior Member
8 posts

Joined: Feb 2006
QUOTE(tiensong @ Sep 8 2011, 10:29 AM)
a) Auto Gate point using 7 core x 2.5mm PVC/SWA/PVC cable buried underground RM450 (per nos)
b) Gate Light point using 2 core x 1.5mm PVC/SWA/PVC cable buried underground RM120 (per nos)
c) Door bell point using 2 core x 1.5mm PVC/SWA/PVC cable burier underground RM120 (per nos)
*
Per nos is per run irregardless of length?

tq for sharing bro
TStiensong
post Sep 8 2011, 03:04 PM

Look at all my stars!!
*******
Senior Member
2,237 posts

Joined: Jul 2011
QUOTE(feeroz @ Sep 8 2011, 02:54 PM)
Per nos is per run irregardless of length?

tq for sharing bro
*
per unit regardless of length..(of course, the length already in their calculation after site measurement/inspection....and the size of project maybe a factor of price too...)



weikee
post Sep 8 2011, 05:17 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
My house armored cable are lay as below

From inside house (at switch faceplate) to Alarm control box (11 core), then 2 unit of 4 core armored from alarm control box to left pillar, and right pillar. From alarm control box, 2 wires to bell, 2 wires to light.
kamion
post Sep 8 2011, 06:28 PM

Casual
***
Junior Member
327 posts

Joined: Feb 2011
QUOTE(tiensong @ Sep 8 2011, 02:14 PM)
Hmm..based on few quotations that I received, all charge separately....
*
Yah, I got charged separately too, but I saw the cable only single 7-core cable running from the house to the gate pillar, and felt a bit cheated that I got charged separately. rclxub.gif
weikee
post Sep 8 2011, 07:49 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
Mine is just one lump sump charge of RM 650 for autogate. Verbally told me 11 core.
phoenix69
post Sep 8 2011, 08:56 PM

Regular
******
Senior Member
1,836 posts

Joined: Sep 2007


QUOTE(weikee @ Sep 8 2011, 07:49 PM)
Mine is just one lump sump charge of RM 650 for autogate. Verbally told me 11 core.
*


Ouch sad.gif
I got charged RM680.00 for 9 cores, Wanna change to 12 core add RM200+ mad.gif
weikee
post Sep 8 2011, 09:18 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
Hmm, got 9 cores? and 12 cores?

Mine is just 11 cores + 4 cores
phoenix69
post Sep 8 2011, 09:42 PM

Regular
******
Senior Member
1,836 posts

Joined: Sep 2007


QUOTE(weikee @ Sep 8 2011, 09:18 PM)
Hmm, got 9 cores? and 12 cores?

Mine is just 11 cores + 4 cores
*
That is what I was told by my wiring contractor blink.gif
True or not dunno... I am just the layman customer. tongue.gif
kamion
post Sep 9 2011, 01:04 PM

Casual
***
Junior Member
327 posts

Joined: Feb 2011
Sigh. I got charged RM650 for the autogate cable, and then RM120 for door bell point and bell push, and RM220 for gate lights and switch. Maybe I can argue with him why he charge so much...............
weikee
post Sep 9 2011, 01:20 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
Why not ask what is inclusive of the price? Some are higher because involve hacking

Mine is this price because they don't have hack the floor, because the floor is tear down and rebuild a concrete floor by my wet work contractor.