power carrying capacity of ac/dc lines
double circuit ac line power, Pac = 6EpIlcosφ
dc line power, Pdc = 6VdId
k = dc withstand voltage/ac withstand voltage (rms)
k1 = ac insulation level/rated ac voltage
k2 = dc insulation level/rated dc voltage
when the lines are loaded to their thermal loadings, and Vd=k*(k1/k2)*Ep
Pdc = 6(k(k1/k2)EpIl)
= k(k1/k2)*(Pac/cosφ)
taking k=1, k1=2.5, k2=1.7 (very conservative assumptions)
therefore, Pdc/Pac=1.47/cosφ
power transmission is at least 47% higher
losses is decreased by 1/1.47 = 68%
edit: i think electrical engineers can confirm that the power transmission and loss decrease can be higher than that, plus the skin effect wasn't taken into account.