power carrying capacity of ac/dc lines

double circuit ac line power, Pac = 6EpIlcosφ
dc line power, Pdc = 6VdId

k = dc withstand voltage/ac withstand voltage (rms)
k1 = ac insulation level/rated ac voltage
k2 = dc insulation level/rated dc voltage

when the lines are loaded to their thermal loadings, and Vd=k*(k1/k2)*Ep

Pdc = 6(k(k1/k2)EpIl)
= k(k1/k2)*(Pac/cosφ)

taking k=1, k1=2.5, k2=1.7 (very conservative assumptions)

therefore, Pdc/Pac=1.47/cosφ

power transmission is at least 47% higher

losses is decreased by 1/1.47 = 68%

edit: i think electrical engineers can confirm that the power transmission and loss decrease can be higher than that, plus the skin effect wasn't taken into account.